Greetings,

I'm trying to input the following 60k BTU/HR ECU (image of specs attached and below) into an EnergyPlus file using the idf editor but I am relatively new to EnergyPlus so I'm having trouble figuring out which values to use for the required EnergyPlus fields.  I apologize in advance if some of these may seem obvious to you and I would greatly appreciate your input. I've gone through the manuals and I'm still having trouble.

The ECU will be used in a single zone 20'x30' building with vinyl sides in very cold temperatures.

The fields which I am unsure of are:
*Type of HVAC equipment I believe would be  PackagedTerminalAirConditioner buy I'm not sure.
*HVACTemplateZone:PTAC (all values)
*Sizing:Parameters (all values)
*Air flow values

ECU DESCRIPTION: 60K BTU/HR - ECU. It is used to cool, dehumidify, heat and filter circulating air in tents and shelters to meet equipment and personnel requirements. The 60K BTU/hr ECU, is self-contained in a single cabinet that is ideally suited for tent installations.  The ECU is designed to circulate, filter, and cool or heat air in the room or enclosure to which it is attached by flexible ducts. The ECU features a variable frequency compressor motor drive to limit in-rush current.

Any suggestions on which fields can be filled in EnergyPlus using these specs below would be of tremendous help.

ECU SPECIFICATIONS (also attached in image) :
*Operating Temperatures: Cooling = 40 to 125°F ; Heating = -50 to 70°F
*Control: Internally or remotely mounted control box
*Power Consumption: Maximum 11.0 kW
*Minimum Power Factor: 0.90
*Dimensions (Max.) 42-inch (L) x 35-inch (W) x 46-inch (H)
*Refrigerant R410A (6.7 lbs (3.04 kg) total charge), non-ozone depleting
*Minimum Evaporator Air Flow 1,700 SCFM
*Compressor Oil type: Compressor Polyester Oil (CPOE)
*Compressor Capacity: 60 oz

*Minimum Cooling Capacity:
- Total: 60,000 Btu/hr (Minimum) Cooling
-Sensible: 45,000 Btu/hr (Minimum) Cooling
-Desired Sensible: 48,000 Btu/hr Cooling
-50 Hz Total: 44,000 Btu/hr (Minimum) Cooling

*Minimum Heating Capacity: Total: 9.94 kW (33,935 Btu/hr)
*Minimum Fresh Air Airflow 280 SCFM

The ECU is designed to automatically maintain the air in the room or enclosure at the desired temperature selected on the remote box assembly.

Thank you very much!

Abe

Abelevbrc@xxxxxxxxx



__._,_.___
View attachments on the web

Posted by: Al BRC <abelevbrc@xxxxxxxxx>


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Visit Your Group
Yahoo! Groups
• Privacy • Unsubscribe • Terms of Use

__,_._,___
Attachment not found:
D:\Eudora\Attach\Shelter_11_18_14.idf
Attachment not found:
D:\Eudora\Attach\ecu specs and image.png