Re: [EnergyPlus_Support] Adding Exhaust Fan





O good, sorry for mis understanding your problem.  ZoneVentilation:DesignFlowRate could also do Exhaust.


Name ZoneVentilation:DesignFlowRate
Zone or ZoneList Name ZoneList
Schedule Name On
Design Flow Rate Calculation Method AirChanges/Hour
Design Flow Rate
Flow Rate per Zone Floor Area
Flow Rate per Person
Air Changes per Hour .35
Ventilation Type Exhaust
Fan Pressure Rise 600
Fan Total Efficiency .82
Constant Term Coefficient 1
Temperature Term Coefficient
Velocity Term Coefficient
Velocity Squared Term Coefficient
Minimum Indoor Temperature -100
Minimum Indoor Temperature Schedule Name
Maximum Indoor Temperature 100
Maximum Indoor Temperature Schedule Name
Delta Temperature -100
Delta Temperature Schedule Name
Minimum Outdoor Temperature -100
Minimum Outdoor Temperature Schedule Name
Maximum Outdoor Temperature 100
Maximum Outdoor Temperature Schedule Name
Maximum Wind Speed 40




â??â??
Jeremiah D. Crossett
 
 | Senior Analyst  | LEED Green Associate 
â??â??
7411 SW Capitol Highway | Portland, OR 97219 
â??â??
 | Mobile 503-688-8951
  




On Wed, Nov 26, 2014 at 12:38 PM, linswoods@xxxxxxxxxxxxxxxx [EnergyPlus_Support] <EnergyPlus_Support@xxxxxxxxxxxxxxx> wrote:
 

Error Solved:


I had defined the nodes in a nodelist as opposed to equipment connections.  Since there was no equipment connections object initially, energyplus failed to see it as a controlled zone.  Thanks again for the help.




__._,_.___

Posted by: Jeremiah Crossett <jcrossett@xxxxxxxxxxxxxxx>


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Visit Your Group
Yahoo! Groups
• Privacy • Unsubscribe • Terms of Use

__,_._,___