Some extracts from ASHRAE Application A05:

“Pool and spa areas should be maintained at a negative pressure of

15 to 40 Pa relative to the outdoors and adjacent areas of the building

to prevent chloramine odor migration”

 

Or better, I am sending the whole chapter.

 

From: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx]
Sent: Tuesday, December 9, 2014 13:57
To: EnergyPlus_Support@xxxxxxxxxxxxxxx
Subject: RE: [EnergyPlus_Support] Pools application

 

 

Great information, Ned.

I'd like to ask a few questions regarding your last paragraph:
- Do you know what is, or where I can find, the recommended negative pressure in swimming pools?
- When you said that at this recommended pressure, infiltration would be 1-2 times the required fresh air ventilation, do you mean that infiltration alone would be 4-8 ACH (1-2 times the 4 ACH recommended by ASHRAE)?
- As long as I understood, you say that most pools don't have in fact negative pressure. Do you have then any idea of what infiltration normally is in common swimming pools?

Thanks,
Rui



__._,_.___
View attachments on the web

Posted by: "Artem Zhukov" <az141208@xxxxxxxxx>


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.





__,_._,___
Attachment not found:
D:\Eudora\Attach\A05 SI_ PLACES OF ASSEMBLY.PDF