Giovani,

There are tons of example files that show you how to set a boiler. Look into the example file folder, there's a spreadsheet that details which example file has what type of system. Typical location is C:\EnergyPlusV8-2-0\ExampleFiles\ExampleFiles.xls

Also, there are HVACTemplate objects to build a boiler plant. HVACTemplate:Plan:Boiler, HVACTemplate:Plant:HotWaterLoop etc... (The Input/Output Reference can help too!)

I suggest you take a look at the example file "HVACTemplate-5ZoneBaseboardHeat.idf" which makes uses of the HVACtemplate objects to build a simple boiler plant.



As far as your other question, I think you may be confused about internal water storage and water flow. Look at your design, or leave it to be autosized for now...

Best,
Julien

--
Julien Marrec, EBCP, BPI MFBA
Energy&Sustainability Engineer
T: +33 6 95 14 42 13

LinkedIn (en) : www.linkedin.com/in/julienmarrec
LinkedIn (fr) : www.linkedin.com/in/julienmarrec/fr


2015-02-12 11:04 GMT+01:00 banidavi@xxxxxxxxxxxx [EnergyPlus_Support] <EnergyPlus_Support@xxxxxxxxxxxxxxx>:
 

Hi everyone, I am performing simulations of an electric boiler. I am using Boiler:HotWater object and my doubt is how to programme the fields Boiler Water Inlet Node Name and Boiler Water Outlet Node Name. Which specific objects should I use in order to operate the boiler (branch, node list, etc)? I didn't find an exemple file correspondent, so maybe an exemple could help me. 

Other question is: I have a domestic boiler of 0.3 liters, what should be my Design Water Flow Ratio in m3/s?


Thank you in advance.

Giovani Dávi

 




__._,_.___

Posted by: Julien Marrec <julien.marrec@xxxxxxxxx>


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Visit Your Group
Yahoo! Groups
• Privacy • Unsubscribe • Terms of Use

__,_._,___