You could be better off opening the IDF file in the Openstudio sketchup plugin, do the modification and then copy the geometry back to your file.

But if you want to do it manually...

Outside Boundary Condition is what you want to look at.

What you want to do is to change any object that is "Surface" (and will have something non-blank for "Outside Boundary Condition Object") to "Adiabatic", leaving the rest intact.


Cheers,
Julien

--
Julien Marrec, EBCP, BPI MFBA
Energy&Sustainability Engineer
T: +33 6 95 14 42 13

LinkedIn (en) : www.linkedin.com/in/julienmarrec
LinkedIn (fr) : www.linkedin.com/in/julienmarrec/fr


2015-02-11 20:36 GMT+01:00 Saad Abobakr sably2003@xxxxxxxxx [EnergyPlus_Support] <EnergyPlus_Support@xxxxxxxxxxxxxxx>:
 

HI Waseem,

Thank you for your help.
If I have zones of three building like the one that I attached, how can I decide the paer of the zone that is connected with the other zone because I want to just to isolate the zones from each other and keep without isolation with outside.

Regards,



On Sunday, February 1, 2015 4:44 PM, "waseem khan waseemshahkhan@xxxxxxxxx [EnergyPlus_Support]" <EnergyPlus_Support@xxxxxxxxxxxxxxx> wrote:


 
Make it Adiabatic see below pic for reference

Inline image 1  

On Sun, Feb 1, 2015 at 11:05 PM, waseem khan <waseemshahkhan@xxxxxxxxx> wrote:
Make the wall adiabatic from building surface detail.
Regards,
Waseem Shah Khan
Energy Analyst & Commission Engg.
Please, consider your environmental responsibility. 
Before printing this e-mail ask yourself: "Do I need a hard copy?"
On Feb 1, 2015 8:21 PM, "Saad Abobakr sably2003@xxxxxxxxx [EnergyPlus_Support]" <EnergyPlus_Support@xxxxxxxxxxxxxxx> wrote:
 
 Hi everybody,

I am using the IDF file that is already available in EnergyPlus examples under name(RadLoTempElecTermReheat) , It is building of three zones and I want to isolate the zones from each other completely, how can I do that?

attached please find the file.

regards,
 




--
â??
Kind Regards,
Waseem Shah Khan
â??Sr.â??Energy Analyst
â??& Commissioning Engineer â??
Riyadh, Saudi Arabia





__._,_.___

Posted by: Julien Marrec <julien.marrec@xxxxxxxxx>


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Visit Your Group
Yahoo! Groups
• Privacy • Unsubscribe • Terms of Use

__,_._,___