|
There is currently no good answer to your question. You are not alone. Until a good answer presents itself, my advise would be to find a "best fit" equipment in the e+ data folder for the required gross rated capacity and use that equipment's curves. Then (hopefully only slightly) adjust the rated gross capacity and gross COP inputs to match your unit. Then accept that the partload performance is slightly better, thus unfortunately benefiting the baseline case. Some of us are working on a solution, but will start with dx cooling coils. Mit freundlichen Grü�en- Sent from my iPhone (excuse the brevity) i. A. Jean Marais b.i.g. bechtold Tel. +49 30 6706662-23 On 19.02.2015, at 15:55, "iluminasol33@xxxxxxxxx [EnergyPlus_Support]" <EnergyPlus_Support@xxxxxxxxxxxxxxx> wrote:
__._,_.___ Posted by: "jeannieboef@xxxxxxxxx" <jeannieboef@xxxxxxxxx> Primary EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button. __,_._,___ |