The core zone loads will be affected by the perimeter zones if there are temperature differences between the zones.
From: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx]
Sent: Thursday, March 05, 2015 2:05 PM
To: EnergyPlus_Support@xxxxxxxxxxxxxxx
Subject: Re: [EnergyPlus_Support] Sensible cooling rate
Yo are right, the ground floor has slab on grade and top floor has a roof. The top floor core zone receives some heat energy from roof too so it should
be more warmer than bottom floor especially at higher set points.
I notice that in the html report, the plug load intensity for the core bottom zone is shown as sum of all the 4 perimeter zones. This error is just in
reporting or for calculating core zone load E+ considers sum of perimeter zone loads?
There are differences ? the bottom floor mmay have a slab on the ground or connected to another space? The top floor has a roof.
The three floors each have their own separate cooling systems. The design conditions for the three cooling systems are same . The three floors are identical.
There is no window ventilation.
The above figures are when cooling set point is 27C and lower ones for 24C.I am unable to understand by raising temp. to 27C bottom core zone starts behaving
differently. Its operating temperatures, PMV go high when all zones cooling set point temperatures have been raised and cooling systems are indentical.
If the air temperature were maintained at the cooling setpoint all the time, then the PMV would be the same in all the zones unless for some reason they
have differing humidities. Are they served by the same AHU? If it is window ventilated, are the ventilation rates equal? AFN would take the building height and stack effect into account. Differing leakage and window ventilation (height dependant) may result
in differing humidities.
PMV is basically a function of operative temperature and humidity. operative temperature is almost the average of the mean radiant and air temps. The
difference must lay with these factors.
Mit freundlichen Grü�en- Sent from my iPhone (excuse the brevity)
On 04.03.2015, at 21:27, "Fakeha Sehar fakeha_s@xxxxxxxxx [EnergyPlus_Support]" <EnergyPlus_Support@xxxxxxxxxxxxxxx> wrote:
I am unable to figure about below
I have three floors, with one core zone and five perimeter zones each. When the core zone cooling set point is 24C, the top floor is slightly more hot
(higher PMV index) as it receives more sunlight, than the mid and bottom floors. Similarly, mid floor has higher PMV index than bottom.
Now when I raise the set point to 27C, I notice that mid floor has the lowest PMV index. Bottom floor has much higher PMV index than mid floor. The sensible
cooling rate is higher than that of mid floor, why? Bottom floor PMV index should still have been the lowest.