[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]

[EnergyPlus_Support] How is Ground defined in EnergyPlus?





We can specify monthly average temperature for the "ground" in EnergyPlus.

But how is this affect the simulation, especially those surfaces touching the ground surface or near it?

I mean we don't need to literally model the ground surface in EnergyPlus, but how dose it affect the thermal environment, such as reflecting solar radiation to building surfaces, radiating heat towards building surfaces when the ground is heated up?

BTW, is there a ground reflection parameter we can adjust in EnergyPlus?

Thank you very much in advance!




__._,_.___

Posted by: hope.zh@xxxxxxxxx


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Visit Your Group
Yahoo! Groups
• Privacy • Unsubscribe • Terms of Use

__,_._,___