To further Ned’s explanation, below are the units connected with each term where Value 1 & 2 are “Heat Capacity” or “Thermal Capacitance” and the term “SpecificHcombine” would
probably be more appropriately represented as “Total (or combined) Heat Capacity” with units of J/K:
Jerry Phelan Codes and Standards Advocate Bayer MaterialScience From: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx]
First you have to assume that what you are blending is evenly mixed, then this should make sense: Volume1 x Density1 x SpecificH1 = Value1 Volume2 x Density2 x SpecificH2 = Value2 SpecificHcombine = (Value1+Value2)/(VolumeCombine x DensityCombine) Ned Lyon, P.E. (MA, WV) SIMPSON GUMPERTZ & HEGER
From:
EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx]
Can anybody please tell me how to calculate combined specific heat of a compound material from two or more values of specific heat of its components.
For example, to calculate specific heat of fly ash brick masonry from value of specific heat of fly ash brick suppose 'x' & value of specific heat of cement mortar suppose 'y'.
The information contained in this e-mail is for the exclusive use of the intended recipient(s) and may be confidential, proprietary, and/or legally privileged. Inadvertent disclosure of this message does not constitute a waiver of any privilege. If you receive this message in error, please do not directly or indirectly use, print, copy, forward, or disclose any part of this message. Please also delete this e-mail and all copies and notify the sender. Thank you. For alternate languages please go to http://bayerdisclaimer.bayerweb.com
__._,_.___ Posted by: Jerry Phelan <jerry.phelan@xxxxxxxxx> Primary EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button. __,_._,___ |