Re: [EnergyPlus_Support] New Feature Request - "Return Air Fraction" and "Exhaust Air Fraction" for Internal Loads?





I propose a summary:
For the reasons above, I have adopted this strategy for designs that use a makeup air unit which discharges its air very close to the exhaust hood:
  1. Create a small, separate zone for the makeup air unit and exhaust (including the hood)  This keeps the heat balance for the kitchen equipment separate from the adjoining kitchen zone.
  2. Control the air loop of the makeup air unit with a constant temperature discharge or outdoor air reset control, whichever is used by the design.
  3. Schedule the makeup / exhaust for actual operating hours.
  4. Assign the kitchen equipment energy (sensible and latent) which is exhausted to an Exterior:FuelEquipment  object so that its energy is accounted for, but does not affect a zone.
  5. Assign the remaining kitchen equipment energy to the main kitchen zone (so that its energy does affect the zone) using OtherEquipment for latent energy)
  6. If heat recovery is part of the design, it can be included in the makeup / exhaust air loop.
There. I have it off my chest and hope it is clear :).  The previous posts on this thread did not seem to capture all of the elements, so I hope this helps condense and organize them.

On Mon, Apr 27, 2015 at 11:39 PM, 'jeannieboef@xxxxxxxxx' jeannieboef@xxxxxxxxx [EnergyPlus_Support] <EnergyPlus_Support@xxxxxxxxxxxxxxx> wrote:
 

Lighting doesn't produce moisture, else it would work.

Mit freundlichen Grü�en- Sent from my iPhone (excuse the brevity)

i. A.
Jean Marais
b.i.g. bechtold

On 27.04.2015, at 23:26, "Jason Quinn jason.e.quinn@xxxxxxxxx [EnergyPlus_Support]" <EnergyPlus_Support@xxxxxxxxxxxxxxx> wrote:

 

Couldn't you just model the kitchen equipment as lighting? i.e. set the power equal. Then you could specify the fraction. I know the meters would be wonky but custom meters are pretty easy to do.

Jason Quinn
+64 21 1846 911

On Tue, Apr 28, 2015 at 12:07 AM, Karen Walkerman kwalkerman@xxxxxxxxx [EnergyPlus_Support] <EnergyPlus_Support@xxxxxxxxxxxxxxx> wrote:
 

Awesome! I'll do that.

On Apr 25, 2015 8:55 AM, "Linda Lawrie linda@xxxxxxxxxxxxxx [EnergyPlus_Support]" <EnergyPlus_Support@xxxxxxxxxxxxxxx> wrote:
 

I believe you can enter a new feature request directly into the github system for EnergyPlus.

At 09:36 AM 4/24/2015, Karen Walkerman kwalkerman@xxxxxxxxx [EnergyPlus_Support] wrote:


I'm currently modeling a few buildings where the design team wants to explore the effectiveness of heat recovery on kitchen exhaust hoods.

In the DOE Commercial Reference Buildings, kitchen cooking equipment - 70% of the energy is modeled as "lost." � Some of this energy is truly "lost" to the food being cooked, but much of it is captured and exhausted by hoods.�  It is not mixed with the zone, but in the model, it is captured by a system and should be modeled as such.

When modeling lights and refrigeration equipment, we are given the option to specify a "return air fraction" - a portion of the heat that is transferred directly to the zone return air.�  It would be awesome if this option were added to the following objects:

ElectricEquipment
GasEquipment
SteamEquipment
HotWaterEquipment
OtherEquipment

It would also be great to have an "Exhaust Air Fraction" option - so that some of the heat generated could be assigned directly to the exhaust air node.

While the need to model kitchen exhaust heat recovery illuminates the limitation within EnergyPlus, it is a limitation in accurately modeling kitchen energy use even without heat recovery.

Thanks!

Karen






--

James V Dirkes II, PE, BEMP, LEED AP
CEO/President
The Building Performance Team Inc.
1631 Acacia Dr, GR, Mi 49504

Direct: 616.450.8653
jim@xxxxxxxxxxxxxxxxxxxxxxxxxxx

Website l  LinkedIn

The truth is still the truth, even if nobody believes it.  A lie is still a lie, even if everyone believes it.



__._,_.___

Posted by: Jim Dirkes <jim@xxxxxxxxxxxxxxxxxxxxxxxxxxx>


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Visit Your Group
Yahoo! Groups
• Privacy • Unsubscribe • Terms of Use

__,_._,___