Re: 2) the embedded pipe (lowtemperatureradiant) model in e+ can't handle being placed between thin (highly conductive) layers of a construction. It needs the thermal diffusivity to be high enough for numerical stability. I thought was that perhaps the same is true for your pipe. I suggest testing it with a thick steal pipe, and further testing with different plastic pipe thicknesses to see how it behaves. Further than looking into the source code and contacting helpdesk support, I have not more to offer for tips. Goodluck, Jean Mit freundlichen Grü�en- Sent from my iPhone (excuse the brevity) i. A. Jean Marais b.i.g. bechtold Tel. +49 30 6706662-23 On 19.05.2015, at 15:35, "robertogrilloait@xxxxxxxxx [EnergyPlus_Support]" <EnergyPlus_Support@xxxxxxxxxxxxxxx> wrote:
__._,_.___ Posted by: "jeannieboef@xxxxxxxxx" <jeannieboef@xxxxxxxxx> Primary EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button. __,_._,___ |