[EnergyPlus_Support] Re: Pipe:Indoor Pipe Fluid against Ambient Heat Transfer Rate [2 Attachments]





Thank you again for your input!

1) I have following figures: pipe length: 13.1 m. Max water flow rate: 0.15 kg/s =1.5 10^-4 m3/s. Pipe inside diameter: 0.05 m, pipe section 2.0 10^-3 m2. Hence, Max water speed: 0.075 m/s. So I comply with the requirement â??fluid cannot manage to pass through the pipe section within a timestepâ?? for a timestep of 1/20 hour, and the particle would stay in the pipe for three timesteps for a timestep of one minute.

With these timesteps, I do get rid of HVAC convergence warnings. However, the curves of pipe ambient/fluid heat transfer rates still look similar (attached screenshots).

 

2) I am not sure what you mean here? Given the material, the thermal diffusivity of the pipe should not be so high:

 

Material,

                distribution-SHSpace Heating  pipe construction plastic,

                Smooth,

                0.004,

                0.4,

                900,

                1200,

                .9,

                .7,

                .7;

 

Material,

                distribution-SHSpace Heating  pipe construction insulation,

                MediumRough,

                0.016667,

                0.035,

                15,

                1500,

                .9,

                .7,

                .7;

 

Construction,

                distribution-SHSpace Heating  pipe construction,

                distribution-SHSpace Heating  pipe construction insulation,

                distribution-SHSpace Heating  pipe construction plastic;




__._,_.___
View attachments on the web

Posted by: robertogrilloait@xxxxxxxxx


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Visit Your Group
Yahoo! Groups
• Privacy • Unsubscribe • Terms of Use

__,_._,___
Attachment Converted: "D:\Eudora\Attach\pipe-ambient-heat-transfer-rate-timestep-60.PNG" Attachment Converted: "D:\Eudora\Attach\pipe-fluid-heat-transfer-rate-timestep-60.PNG"