Jin,
It does not make sense to use a VRF, which is inherently a multi-zone system, for DOAS because all of the benefit of VRF comes from refrigerant management among several zones.

Nonetheless, if that's what you have, VRF is essentially a heat pump for its cooling and heating functions.  Try modeling the DOAS as a heat pump with performance curves that match your VRF.

On Thu, May 21, 2015 at 11:11 PM, sangjin722@xxxxxxxxx [EnergyPlus_Support] <EnergyPlus_Support@xxxxxxxxxxxxxxx> wrote:
 

Hi, Jeremiah

It seems that you misunderstood the system which I said.

 

It is right that there are VRF indoor unit located in each zone to supply the cooling/heating air and the outdoor air is from a dedicated outdoor air system.

But the outdoor air is from another VRF indoor unit, not a general AHU. The outdoor air is directly supplied into each zone by a duct which connected to this indoor unit.

 

Do you have any idea to model this system?

Thanks.

 

- Jin

 

 




--

James V Dirkes II, PE, BEMP, LEED AP
CEO/President
The Building Performance Team Inc.
1631 Acacia Dr, GR, Mi 49504

Direct: 616.450.8653
jim@xxxxxxxxxxxxxxxxxxxxxxxxxxx

Website l  LinkedIn

The truth is still the truth, even if nobody believes it.  A lie is still a lie, even if everyone believes it.



__._,_.___

Posted by: Jim Dirkes <jim@xxxxxxxxxxxxxxxxxxxxxxxxxxx>


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Visit Your Group
Yahoo! Groups
• Privacy • Unsubscribe • Terms of Use

__,_._,___