[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]

Re: [EnergyPlus_Support] Standard 62.1 Summary





JIm,

try using the 

VentilationRateProcedure;                                !- System Outdoor Air Method

in the Sizing:System object


Cheers,




On Tuesday, June 16, 2015 3:54 PM, "Jim Dirkes jim@xxxxxxxxxxxxxxxxxxxxxxxxxxx [EnergyPlus_Support]" <EnergyPlus_Support@xxxxxxxxxxxxxxx> wrote:


 
Dear Forum,
I don't use the Standard62.1 Table report normally, but am trying to do so.  I have it specified in my IDF, and while the report gets produced, all of the table cells are blank.

I suspect that there is another object on which the Table depends for values, but I am already using the obvious one (DesignSpecification:OutdoorAir)

Can one of you suggest what I might be missing?  Thanks in advance.

--
James V Dirkes II, PE, BEMP, LEED AP
CEO/President
The Building Performance Team Inc.
1631 Acacia Dr, GR, Mi 49504

Direct: 616.450.8653
jim@xxxxxxxxxxxxxxxxxxxxxxxxxxx

Website l  LinkedIn
Studies show that four out of every three people have a hard time with math.




__._,_.___

Posted by: Vladimir Bajic <bajic.vladimir@xxxxxxxxx>


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Visit Your Group
Yahoo! Groups
• Privacy • Unsubscribe • Terms of Use

__,_._,___