[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]

[EnergyPlus_Support] Illegal control type for Zone Error





Hi all ,

I keep getting the following error when I added my thermostat to SPACE1-1 :


 Severe  ** GetZoneAirSetpoints: Illegal control type for Zone=SPACE1-1, Found value=24, in Schedule=CLG-SETP-SCH

   **   ~~~   ** ..valid range values are [0,4].

What does that mean  , and how can I eleminate this error ? Note : I reset the schedule limits to be 

from 0 to 100\

please help

thanks in advance





__._,_.___

Posted by: a.aelhefni@xxxxxxxxx


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Visit Your Group
Yahoo! Groups
• Privacy • Unsubscribe • Terms of Use

__,_._,___