Re: [EnergyPlus_Support] Illegal control type for Zone Error





The "control type" is not a temperature setpoint.  Rather, it tells E+ what type of thermostat is in use.  (see a thermostat example and the excerpt from the Input Output reference p1222 below)

Inline image 1
Inline image 2

On Fri, Jul 24, 2015 at 6:07 AM, a.aelhefni@xxxxxxxxx [EnergyPlus_Support] <EnergyPlus_Support@xxxxxxxxxxxxxxx> wrote:
 

Hi all ,

I keep getting the following error when I added my thermostat to SPACE1-1 :


 Severe  ** GetZoneAirSetpoints: Illegal control type for Zone=SPACE1-1, Found value=24, in Schedule=CLG-SETP-SCH

   **   ~~~   ** ..valid range values are [0,4].

What does that mean  , and how can I eleminate this error ? Note : I reset the schedule limits to be 

from 0 to 100\

please help

thanks in advance






--

James V Dirkes II, PE, BEMP, LEED AP
CEO/President
The Building Performance Team Inc.
1631 Acacia Dr, GR, Mi 49504

Direct: 616.450.8653
jim@xxxxxxxxxxxxxxxxxxxxxxxxxxx

Website l  LinkedIn

Life is not easy.  Itâ??s never been easy. Expecting it to be easy is not a healthy attitude.
Relax. Refresh. Regroup. Carry on.



__._,_.___

Posted by: Jim Dirkes <jim@xxxxxxxxxxxxxxxxxxxxxxxxxxx>


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Visit Your Group
Yahoo! Groups
• Privacy • Unsubscribe • Terms of Use

__,_._,___