[EnergyPlus_Support] Re: ZoneControl:Humidistat_** Severe ** ZoneControl:Humidistat Zone Name duplicate name=71E478, AND GetStagedDualSetpoint: invalid names





Junia

You don't need to use a separate Zone Humidistat object, you can specify it in the same IdealLoads object as Humidification and Dehumidification setpoints True that this only allows for a fixed setpoint, and that it conflicts with what is documented in the I/O Manual. I changed it and it run fine, I also run it under other E+ versions, changed names etc, and the only thing that crashes is when you use the Humidistat object. 

Enjoy
Luis