Re: [EnergyPlus_Support] Warning: GetSurfaceData: InterZone Surface Azimuths do not match as expected





Hi Simona,

I've not used the Open Studio plugin so I don't know how it interprets the facing direction of the Sketchup surfaces, but give it a try ans see what it does.  I use the gModeller plugin to generate IDF files, this takes all the surfaces that make up a zone and works out which is the inside and outside face of each relative to the zone and then puts the points in the correct order.

Regards
Donald

Donald MacSween
Energy Consultant
GreenspaceLive
______________________________________________   

 T. +44(0)1851 707876          M. +44 (0) 7708 339647
W. www.greenspacelive.com
______________________________________________   

On Wed, Jul 29, 2015 at 4:44 PM, Simona Vasinton simov8@xxxxxxxxx [EnergyPlus_Support] <EnergyPlus_Support@xxxxxxxxxxxxxxx> wrote:
 

Many thanks Donald. I checked the I/O reference and the Tpis and Tricks. I will try to fix it using the reverse face command in Sketchup. Does it make sense? I am looking for a quick way to solve it from the sketchup model without redrawing all the spaces. The error arose because I mirrored one of the apartment of the typical floor plan of my case study. 

Reagards

Simona



On Wednesday, July 29, 2015 11:32 AM, "Donald MacSween donald.macsween@xxxxxxxxxxxxxxxxxx [EnergyPlus_Support]" <EnergyPlus_Support@xxxxxxxxxxxxxxx> wrote:


 
The azimuth of one side of the door should be the opposite of the other side.  e.g. if the door surface in the bathroom zone has azimuth 250 then  the door surface in the corridor zone should have azimuth 70 (250degrees-180degrees).  The facing direction of a surface depends on the order in which the co-ordinates are defined (clockwise or anti-clockwise).  The two sides of the same door will have the same coordinates but defined reverse order.

When viewed from outside their zone, all surfaces will have coordinates defined in the order determined by GlobalGeometryRules.

See the E+ Input/Output Reference for a better description.

Regards
Donald

Donald MacSween
Energy Consultant
GreenspaceLive
______________________________________________   

 T. +44(0)1851 707876          M. +44 (0) 7708 339647
W. www.greenspacelive.com
______________________________________________   

On Tue, Jul 28, 2015 at 9:45 PM, Simona Vasinton simov8@xxxxxxxxx [EnergyPlus_Support] <EnergyPlus_Support@xxxxxxxxxxxxxxx> wrote:
 
Hi
I created the model geometry in sketchup 2015 using the OpenStudio Legacy Plugin and edited it in EnergyPlus 8.2. 
I matched all the surfaces and defined the boundary conditions for all the adjacent zones but for few of them the following warning appears:

 ** Warning ** GetSurfaceData: InterZone Surface Azimuths do not match as expected.
   **   ~~~   **   Azimuth=250.0, Tilt=90.0, in Surface=U5_CORRIDOR_INT_DOOR_S-BATHROOM, Zone=U5_CORRIDOR
   **   ~~~   **   Azimuth=250.0, Tilt=90.0, in Surface=U6_BATHROOM_INT_DOOR_N-CORRIDOR, Zone=U4_BATHROOM
   **   ~~~   ** ..surface class of first surface=Door
   **   ~~~   ** ..surface class of second surface=Door

I have checked the model several times but I can't find the eorror, is this relevant?

Many thanks for your help

Simona






__._,_.___

Posted by: Donald MacSween <donald.macsween@xxxxxxxxxxxxxxxxxx>


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.