Hello Francesko, If I understood properly the difference in VAV ACB and CAV ACB is that first one have some kind of adjustable nozzles geometry and hence are able to maximize induction coefficient at low primary air flows. It seems such VAV ACB are presented in Halton, LTG and Dadanco portfolio (not sure at 100%). But from other side it could be that any CAV ACB could work in VAV (here DCV more appropriate I assume) DOAS but just would call for more fresh air. In this, more straight forward case, you need to create a schedule of primary air as a function of a cooling/heating demand (I think it is a task for EMS work around with schedules). Example: once you know a cooling demand (i.e. sensible (1365+3080) Btuh), then min fresh air should be 55 CFM for 4 foot coil ( what means 55/60 = 0.92 value in outdoor air schedule). It should be calculated for each timestep. ARTEM ZHUKOV | REMAK TEAM | HVAC/Mech.Engineer | Building Performance Engineer | Sustainability Engineer | HVAC TPM | M: +420 774 081 898 | S | IN | T | From: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] Thank you very much. az141208, I haven't found online the graph relative to VAV cooled beams. Do you have an address where I could see it, please? The system is not completely designed yet. I should discuss with the designers the properties of the cooled beams and how they are going to be controlled in order to understand how I should model the "virtual fan coil". Best Regards Francesco
Dear all, Once the DOAS will be established based on occupancy it means that you will have an airflow pattern on your ACB based on occupancy schedule, but you need to have it based on a zone required cooling or heating capacity (because something should induce this secondary air in ACB. This means DOAS should be driven by two parameters: fresh air for people and required cooling capacity. Once required cooling capacity is not zero, but occupancy is zero, then Energyplus should send such amount of fresh air which will satisfy demand of ACB. For VAV ACB there is a graphs which shows dependency between ratio of cooling capacity/ max cooling capacity @ max primary airflow and the ratio of primary airflow/max primary airflow. So a schedule of minimum amount of fresh air should respect that. From: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] Francesco, I think you are suggesting:
Assuming that the fan coil fan energy is ~0 (because a chilled beam has no fan), and the pump energy for the fan coils is about the same as for chilled beams ... that sounds like a nice solution. Part of your challenge will be to establish zones and zone scheduling in such a way as to represent the occupant diversity properly. You want the VAV box to actually turn OFF (zero flow) when no one is in the room, so you can't just use a fractional diversity schedule (values 0 - 1.0). I think it must be either 0 or 1, no in-between values. I did something similar a while ago for a hotel which had room HVAC interlocked with whether the room was rented or not. I made some assumptions about the occupancy rates and made sure some of the rooms were completely off / unoccupied, while others were on a regular schedule. On Tue, Sep 8, 2015 at 9:32 AM, fpasserini.tn@... [EnergyPlus_Support] <EnergyPlus_Support@xxxxxxxxxxxxxxx> wrote:
-- __._,_.___ Posted by: "Artem Zhukov" <AZ141208@xxxxxxxxx> Primary EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button. __,_._,___ |