Re: [EnergyPlus_Support] Autosized DOAS coil doesn't work





Try adding a second DX coil in series with the first.  Each of these two coils can be assigned a capacity consistent with the flow / watt limits, so you can get double the capacity of a single coil.

On Tue, Nov 10, 2015 at 9:51 AM, cnkhanh1986@xxxxxxxxx [EnergyPlus_Support] <EnergyPlus_Support@xxxxxxxxxxxxxxx> wrote:
 

Hello,

I get fatal error when try so setup DOAS system. This error was confirmed at Fully autosized DX coil should not fail with a fatal SHR error · Issue #4853 · NREL/EnergyPlus. I would like to know how to bypass this error in my case please see my case in here : DOASDXCOIL_wADPBFMethodDCV5outdoortest1DOAS.idf at the moment. In my case the DX coil should get 36 kW at peak condition however due to DX evaporator flow rate limit : < 13 kW.

T

 

Fully autosized DX coil should not fail with a fatal SHR...
User file failing with this error: ** Severe ** Coil:Cooling:DX:SingleSpeed "CORRIDOR_FLR_3_DXCOIL" -- coil bypass factor calculation did not conver...
Preview by Yahoo

 




--

James V Dirkes II, PE, BEMP, LEED AP
CEO/President
The Building Performance Team Inc.
1631 Acacia Dr, GR, Mi 49504

Direct: 616.450.8653
jim@xxxxxxxxxxxxxxxxxxxxxxxxxxx

Website l  LinkedIn

We will forever be crippled if we let emotion or unexamined reactions govern our thoughts and actions. 



__._,_.___

Posted by: Jim Dirkes <jim@xxxxxxxxxxxxxxxxxxxxxxxxxxx>


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Visit Your Group
Yahoo! Groups
• Privacy • Unsubscribe • Terms of Use

__,_._,___