Are you using the CTF solving method? Try decrease the time step to 1 min (i.e. 60 per hour). Check the thermal diffusivity of each layer in the construction does not fall outside the limits.

On 26 Dec 2015 4:47 pm, "alyelhefni@xxxxxxxxx [EnergyPlus_Support]" <EnergyPlus_Support@xxxxxxxxxxxxxxx> wrote:
 

Hi all ,

I have the following sevre error appearing :

________________________________________________

Temperature (high) out of bounds (200.15] for zone="ZONE ONE", for surface="ZN001:CEILING"

   **   ~~~   **  During Warmup, Environment=ALEX_DESIGN_DAY HVAC Sizing Pass 1, at Simulation time=06/03 08:10 - 08:11

   **   ~~~   ** Zone="ZONE ONE", Diagnostic Details:

   **   ~~~   ** ...Internal Heat Gain [92.354] W/m2

   **   ~~~   ** ...Infiltration/Ventilation [1.320] m3/s

   **   ~~~   ** ...Mixing/Cross Mixing [0.000] m3/s

   **   ~~~   ** ...Zone is part of HVAC controlled system.

   **  Fatal  ** CalcHeatBalanceInsideSurf: Program terminates due to preceding conditions.

________________________________________________


I've modified warm up days to 365 days , changed all no mass materials to materials having mass and even tried decreasing internal loads to 0.001 watt and still this error appears .

How can I solve this issue ?




__._,_.___

Posted by: Jean Marais <jeannieboef@xxxxxxxxx>


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Visit Your Group
Yahoo! Groups
• Privacy • Unsubscribe • Terms of Use

__,_._,___