[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]

Re: [EnergyPlus_Support] Output:Table:Monthly question EnergyPlus version 7.0





Perhaps try the allsummary report.

On 19 Jan 2016 12:06 am, "'Jones, Christopher' Christopher.r.Jones@xxxxxxxxxxxx [EnergyPlus_Support]" <EnergyPlus_Support@xxxxxxxxxxxxxxx> wrote:
 

I am a newbie to EnergyPlus.

 

I am working with the ADEG EnergyPlus models and the Commercial Reference Building EnergyPlus models. I noticed that the Commercial Building EnergyPlus model HTML results report includes the Zone Interior Electric loads in a monthly table report. The AEDG model HTML results table doesnâ??t include this report. In comparing the IDFs, I found the following in the ASHRAE90.1_SchoolSecondary_STD2013_Chicago.idf file:

 

Output:Table:Monthly,

  Building Loads - Electric,  !- Name

  2,                       !- Digits After Decimal

  Zone Lights Electric Energy,  !- Variable or Meter 1 Name

  SumOrAverage,            !- Aggregation Type for Variable or Meter 1

  Zone Lights Electric Energy,  !- Variable or Meter 2 Name

  Maximum,                 !- Aggregation Type for Variable or Meter 2

  Zone Electric Equipment Electric Energy,  !- Variable or Meter 3 Name

  SumOrAverage,            !- Aggregation Type for Variable or Meter 3

  Zone Electric Equipment Electric Energy,  !- Variable or Meter 4 Name

  Maximum;                 !- Aggregation Type for Variable or Meter 4

 

Assuming that this is the code that adds the Zone Interior Electric loads report, I copied that bit into the ADEG model input file. After running, the zone tables arenâ??t included in the HTML report.

 

Note the ASHRAE90.1_SchoolSecondary_STD2013_Chicago.idf was run with version 8.0. I am using version 7.0 as that is what the AEDG model was run with.

 

Is there something else I have to add to the input file to get those zone reports to show up?

 

 

Thanks!

 

cid:image003.png@01D09C46.E75BA0D0

Christopher Jones, P.Eng.
Senior Engineer

 

WSP Canada Inc.

2300 Yonge Street, Suite 2300

Toronto, ON M4P 1E4
T +1 416-644-4226

F +1 416-487-9766

C +1 416-697-0056

 

www.wspgroup.com

 



You are receiving this communication because you are listed as a current WSP contact. Should you have any questions regarding WSPâ??s electronic communications policy, please consult our Anti-Spam Commitment www.wspgroup.com/casl. For any concern or if you believe you should not be receiving this message, please forward this message to us at caslcompliance@xxxxxxxxxxxx so that we can promptly address your request. This message is intended only for the use of the individual or entity to which it is addressed, and may contain information which is privileged, confidential, proprietary or exempt from disclosure under applicable law. If you are not the intended recipient or the person responsible for delivering the message to the intended recipient, you are strictly prohibited from disclosing, distributing, copying or in any way using this message. If you have received this communication in error, please notify the sender, and destroy and delete any copies you may have received.

WSP provides professional land surveying services through the following entities: WSP Surveys (AB) Limited Partnership and WSP Surveys (BC) Limited Partnership



__._,_.___

Posted by: Jean Marais <jeannieboef@xxxxxxxxx>


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Visit Your Group
Yahoo! Groups
• Privacy • Unsubscribe • Terms of Use

__,_._,___