[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]

Re: [EnergyPlus_Support] Refrigeration Energy Increase by Adding DOAS on HVAC System





Hi Tilek, 

Thanks for the answer. I already checked the average temperature and humidity ratio between the two results. And you are true, the temperature and humidity ratio in retail zone increase after adding DOAS into the system, it causes the display case energy increase. This temperature increases because the DOAS supply air setpoint is higher than the zone temperature (actually, the cooling system is off because the zone temperature is below cooling setpoint).  I just realized  that outdoor air flow rate to the zone only works if the HVAC system is in on condition. But I have another question, if I want to make different system, ventilation with unconditioned air (using outdoor air temperature), how can I model it? I am thinking about using ZoneVentilation:DesignFlowRate, Will energyplus include this object to calculate the zone cooling load?

Thanks! 


__._,_.___

Posted by: hidayah.annisanurul@xxxxxxxxx


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Visit Your Group
Yahoo! Groups
• Privacy • Unsubscribe • Terms of Use

__,_._,___