Dear Surya,
In addition to the necessary HVAC system settings, I think that you need is two class list in you IDF file, the "run period" and â??output:variableâ??. The outputs may be in energy (J) or rate (W).
For example:
!- =========== ALL OBJECTS IN CLASS: RUNPERIOD ===========
RunPeriod,
SpecificDay, !- Name
1, !- Begin Month
17, !- Begin Day of Month
1, !- End Month
17, !- End Day of Month
UseWeatherFile, !- Day of Week for Start Day
No, !- Use Weather File Holidays and Special Days
No, !- Use Weather File Daylight Saving Period
Yes, !- Apply Weekend Holiday Rule
Yes, !- Use Weather File Rain Indicators
Yes, !- Use Weather File Snow Indicators
1; !- Number of Times Runperiod to be Repeated
!- =========== ALL OBJECTS IN CLASS: OUTPUT:VARIABLE ===========
Output:Variable,
*, !- Key Value
Zone Air System Sensible Cooling Energy, !- Variable Name
Hourly; !- Reporting Frequency
Output:Variable,
*, !- Key Value
Zone Air System Sensible Cooling Rate, !- Variable Name
Hourly; !- Reporting Frequency
Carlos Krebs
LEED® Accredited Professional
Auditor Interno ISO 14.001
Consultor de Eficiência
Energética em Edificações
Dear all,
I want to get cooling load of every hour in a particular day of a building. How do I get these data of every hour? Please help.
Thanks,