[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]

Re: [EnergyPlus_Support] Input energy plus





Yulia, the idf file is just a text file where you define the objects. The IDFeditor helps us to see the IDF in a more readable way.
But you have to follow the structure.
Try first to include the schedule which Richard gave you using the IDFeditor and then open the IDF file again using Notepad,for example, and you can figure out is the same.
Hope this helps

El 26/02/2016 17:02, "Yulia Puspasari yuliapuspasari86@xxxxxxxxx [EnergyPlus_Support]" <EnergyPlus_Support@xxxxxxxxxxxxxxx> escribió:
 

Is it input to text editor ? How about input to idf editor? 

Example : 

Name                                          OCCUPY-1
Schedule Type Limits Name  Fraction,                
Field1    Through: 12/31
Field2  For: AllDays
Field3.  Until: 8:00
Field4.  9
Field 5   Until: 9:00
Field 6.  7
 Field7. Until: 14:00
 Field8    25
 Field9.   Until: 19:00
 Field10  6

How about that ? It is right or wrong if i am input this in idf editor?


 

Very compact:

Schedule:Compact,
    System Availability Schedule,  !- Name
    Any Number,              !- Schedule Type Limits Name
    THROUGH: 12/31,          !- Field 1
    FOR: AllDays,            !- Field 2
    UNTIL: 24:00, 1;         !- Field 4

Schedule:Compact,
    Fan Availability Schedule,  !- Name
    Any Number,              !- Schedule Type Limits Name
    THROUGH: 12/31,          !- Field 1
    FOR: AllDays,            !- Field 2
    UNTIL: 12:00, 1,         !- Field 4
    UNTIL: 24:00, 0;         !- Field 6

Less compact:

  Schedule:Compact,
    INFIL-SCH,               !- Name
    Fraction,                !- Schedule Type Limits Name
    Through: 3/31,           !- Field 1
    For: AllDays,            !- Field 2
    Until: 24:00,1.0,        !- Field 3
    Through: 10/31,          !- Field 5
    For: AllDays,            !- Field 6
    Until: 24:00,0.0,        !- Field 7
    Through: 12/31,          !- Field 9
    For: AllDays,            !- Field 10
    Until: 24:00,1.0;        !- Field 11

  Schedule:Compact,
    OCCUPY-1,                !- Name
    Fraction,                !- Schedule Type Limits Name
    Through: 12/31,          !- Field 1
    For: WeekDays SummerDesignDay CustomDay1 CustomDay2, !- Field 2
    Until: 8:00,0.0,         !- Field 3
    Until: 11:00,1.00,       !- Field 5
    Until: 12:00,0.80,       !- Field 7
    Until: 13:00,0.40,       !- Field 9
    Until: 14:00,0.80,       !- Field 11
    Until: 18:00,1.00,       !- Field 13
    Until: 19:00,0.50,       !- Field 15
    Until: 24:00,0.0,        !- Field 17
    For: Weekends WinterDesignDay Holiday, !- Field 19
    Until: 24:00,0.0;        !- Field 20


On 2/25/2016 10:08 PM, yuliapuspasari86@xxxxxxxxx [EnergyPlus_Support] wrote:
Hai ,i have some problem to input schedule compact in energyplus. Can everyone give me example to input in energyplus?thanks


------------------------------------
Posted by: yuliapuspasari86@xxxxxxxxx
------------------------------------


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx


The primary EnergyPlus web site is found at:
http://www.energyplus.gov


The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/


Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.


EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.


------------------------------------


Yahoo Groups Links


<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/


<*> Your email settings:
    Individual Email | Traditional


<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)


<*> To change settings via email:
    EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx


<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx



<*> Your use of Yahoo Groups is subject to:
    https://info.yahoo.com/legal/us/yahoo/utos/terms/





-- 
Richard Raustad
Florida Solar Energy Center
1679 Clearlake Road
Cocoa, FL 32922
Ph: (321)638-1454
http://www.fsec.ucf.edu/en/


Program Director
Electric Vehicle Transportation Center
http://evtc.fsec.ucf.edu/



__._,_.___

Posted by: Nacho Gomis <nachogo27@xxxxxxxxx>


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Visit Your Group
Yahoo! Groups
• Privacy • Unsubscribe • Terms of Use

__,_._,___