You can use either. Yes, you can enter your values into the IDF Editor. Don't specify "fraction" for use with occupancy (fractions are 0.0 - 1.0). Use AnyNumber instead. Don't forget to include up through hour 24. Also, there will be 9 people from midnight until 9 AM unless you include a 0 before 9 AM. Look at some example files to get a better idea of the information needed for compact schedules. You can paste this directly into an input file using a text editor, or you can enter these data using the IDF Editor. Schedule:Compact, OCCUPY-1, !- Name AnyNumber, !- Schedule Type Limits Name Through:
12/31, !- Field 1
For: AllDays, !- Field 2 Until: 7:00, !- Field 3 0, !- Field 4 Until: 8:00, !- Field 5 9, !- Field 6 Until:
9:00, !- Field 7
7, !- Field 8 Until: 14:00, !- Field 9 25, !- Field 10 Until: 19:00, !- Field 11 6, !- Field 12 Until:
24:00, !- you forgot the last entry that completes the
entire day
0; !- and a value for that time period (from 19 to 24...and a semicolon for the last entry if using a text editor) You will also need a ScheduleTypeLimits object: ScheduleTypeLimits, Any Number; !- Name On 2/26/2016 11:00 AM, Yulia Puspasari
yuliapuspasari86@xxxxxxxxx [EnergyPlus_Support] wrote:
Is it input to text editor ? How about input to idf editor? -- Richard Raustad Florida Solar Energy Center 1679 Clearlake Road Cocoa, FL 32922 Ph: (321)638-1454 http://www.fsec.ucf.edu/en/ Program Director Electric Vehicle Transportation Center http://evtc.fsec.ucf.edu/ __._,_.___ Posted by: Richard Raustad <rraustad@xxxxxxxxxxxx> Primary EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button. __,_._,___ |