Re: [EnergyPlus_Support] Input energy plus





Ok i will try this to my simulation. Do you have an ID LINE? I think i need your help if i get some errors again and i can send you a pict about that error by LINE.thank you

Sent from Yahoo Mail on Android

On Fri, Feb 26, 2016 at 23:44, Richard Raustad RRaustad@xxxxxxxxxxxx [EnergyPlus_Support]
<EnergyPlus_Support@xxxxxxxxxxxxxxx> wrote:
 

You can use either. Yes, you can enter your values into the IDF Editor. Don't specify "fraction" for use with occupancy (fractions are 0.0 - 1.0). Use AnyNumber instead. Don't forget to include up through hour 24. Also, there will be 9 people from midnight until 9 AM unless you include a 0 before 9 AM.
Look at some example files to get a better idea of the information needed for compact schedules.

You can paste this directly into an input file using a text editor, or you can enter these data using the IDF Editor.

Schedule:Compact,
OCCUPY-1, !- Name
AnyNumber, !- Schedule Type Limits Name

Through: 12/31, !- Field 1
For: AllDays, !- Field 2
Until: 7:00,   !- Field 3
0,                   !- Field 4

Until: 8:00,   !-
Field 5
9,                   !- Field 6
Until: 9:00,   !- Field 7
7,                   !- Field 8
Until: 14:00, !- Field 9
25,                 !- Field 10
Until: 19:00, !- Field 11
6,                    !- Field 12
Until: 24:00,        !- you forgot the last entry that completes the entire day
0;          !- and a value for that time period (from 19 to 24...and a semicolon for the last entry if using a text editor)

You will also need a ScheduleTypeLimits object:

ScheduleTypeLimits,
Any Number;              !- Name



On 2/26/2016 11:00 AM, Yulia Puspasari yuliapuspasari86@xxxxxxxxx [EnergyPlus_Support] wrote:
Is it input to text editor ? How about input to idf editor? 
Example : 

Name                                          OCCUPY-1
Schedule Type Limits Name  Fraction,                
Field1    Through: 12/31
Field2  For: AllDays
Field3.  Until: 8:00
Field4.  9
Field 5   Until: 9:00
Field 6.  7
 Field7. Until: 14:00
 Field8    25
 Field9.   Until: 19:00
 Field10  6

How about that ? It is right or wrong if i am input this in idf editor?


 

Very compact:

Schedule:Compact,
    System Availability Schedule,  !- Name
    Any Number,              !- Schedule Type Limits Name
    THROUGH: 12/31,          !- Field 1
    FOR: AllDays,            !- Field 2
    UNTIL: 24:00, 1;         !- Field 4

Schedule:Compact,
    Fan Availability Schedule,  !- Name
    Any Number,              !- Schedule Type Limits Name
    THROUGH: 12/31,          !- Field 1
    FOR: AllDays,            !- Field 2
    UNTIL: 12:00, 1,         !- Field 4
    UNTIL: 24:00, 0;         !- Field 6

Less compact:

  Schedule:Compact,
    INFIL-SCH,               !- Name
    Fraction,                !- Schedule Type Limits Name
    Through: 3/31,           !- Field 1
    For: AllDays,            !- Field 2
    Until: 24:00,1.0,        !- Field 3
    Through: 10/31,          !- Field 5
    For: AllDays,            !- Field 6
    Until: 24:00,0.0,        !- Field 7
    Through: 12/31,          !- Field 9
    For: AllDays,            !- Field 10
    Until: 24:00,1.0;        !- Field 11

  Schedule:Compact,
    OCCUPY-1,                !- Name
    Fraction,                !- Schedule Type Limits Name
    Through: 12/31,          !- Field 1
    For: WeekDays SummerDesignDay CustomDay1 CustomDay2, !- Field 2
    Until: 8:00,0.0,         !- Field 3
    Until: 11:00,1.00,       !- Field 5
    Until: 12:00,0.80,       !- Field 7
    Until: 13:00,0.40,       !- Field 9
    Until: 14:00,0.80,       !- Field 11
    Until: 18:00,1.00,       !- Field 13
    Until: 19:00,0.50,       !- Field 15
    Until: 24:00,0.0,        !- Field 17
    For: Weekends WinterDesignDay Holiday, !- Field 19
    Until: 24:00,0.0;        !- Field 20


On 2/25/2016 10:08 PM, yuliapuspasari86@xxxxxxxxx [EnergyPlus_Support] wrote:
Hai ,i have some problem to input schedule compact in energyplus. Can everyone give me example to input in energyplus?thanks


------------------------------------
Posted by: yuliapuspasari86@xxxxxxxxx
------------------------------------


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx


The primary EnergyPlus web site is found at:
http://www.energyplus.gov


The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/


Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.


EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.


------------------------------------


Yahoo Groups Links


<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/


<*> Your email settings:
    Individual Email | Traditional


<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)


<*> To change settings via email:
    EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx


<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx



<*> Your use of Yahoo Groups is subject to:
    https://info.yahoo.com/legal/us/yahoo/utos/terms/





-- 
Richard Raustad
Florida Solar Energy Center
1679 Clearlake Road
Cocoa, FL 32922
Ph: (321)638-1454
http://www.fsec.ucf.edu/en/


Program Director
Electric Vehicle Transportation Center
http://evtc.fsec.ucf.edu/

-- 
Richard Raustad
Florida Solar Energy Center
1679 Clearlake Road
Cocoa, FL 32922
Ph: (321)638-1454
http://www.fsec.ucf.edu/en/

Program Director
Electric Vehicle Transportation Center
http://evtc.fsec.ucf.edu/


__._,_.___

Posted by: Yulia Puspasari <yuliapuspasari86@xxxxxxxxx>


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.