Re: [EnergyPlus_Support] Error message





Post your EMS code, please.

On 29 Feb 2016 4:51 pm, "Fakeha Sehar fakeha_s@xxxxxxxxx [EnergyPlus_Support]" <EnergyPlus_Support@xxxxxxxxxxxxxxx> wrote:
 

My heating and cooling set points are as follows: 

Schedule:Compact,
    HtgSetP_Sch,             !- Name
    Temperature,             !- Schedule Type Limits Name
    Through: 12/31,          !- Field 1
    For: Weekdays Saturday,  !- Field 2
    Until: 05:00,15.6,       !- Field 3
    Until: 24:00,21.0,       !- Field 5
    For: Sunday,             !- Field 7
    Until:  5:00,15.6,       !- Field 8
    Until: 22:00,21.0,       !- Field 10
    Until: 24:00,15.6,       !- Field 12
    For SummerDesignDay,     !- Field 14
    Until: 24:00,15.6,       !- Field 15
    For WinterDesignDay,     !- Field 17
    Until: 24:00,21.0,       !- Field 18
    For: AllOtherDays,       !- Field 20
    Until: 24:00,21.0;       !- Field 21

  Schedule:Compact,
    ClgSetP_Sch,             !- Name
    Temperature,             !- Schedule Type Limits Name
    Through: 12/31,          !- Field 1
    For: Weekdays Saturday,  !- Field 2
    Until: 05:00,30.0,       !- Field 3
    Until: 24:00,24.0,       !- Field 5
    For: Sunday,             !- Field 7
    Until: 05:00,30.0,       !- Field 8
    Until: 22:00,24.0,       !- Field 10
    Until: 24:00,30.0,       !- Field 12
    For SummerDesignDay,     !- Field 14
    Until: 24:00,24.0,       !- Field 15
    For WinterDesignDay,     !- Field 17
    Until: 24:00,30.0,       !- Field 18
    For: AllOtherDays,       !- Field 20
    Until: 24:00,30.0;       !- Field 21

I am increasing my cooling set point by 3C using EMS, I can't understand why cooling setpoint is being considered 0 by E+ as indicated by the error message??


On Friday, February 26, 2016 12:36 AM, "Jean Marais jeannieboef@xxxxxxxxx [EnergyPlus_Support]" <EnergyPlus_Support@xxxxxxxxxxxxxxx> wrote:


 
The heating setpoint (HtgSP) is greater than the cooling setpoint (ClgSP). For example, your HtgSP and ClgSP are 20 and 21 respectively (deadband = 1 C), then in your EMS you change to HtgSP = 22 --> error. You must also raise your ClgSP so that it is bigger than the HtgSP. The restriction prohibits sinultanious heating and cooling.
On 25 Feb 2016 9:12 pm, "Fakeha Sehar fakeha_s@xxxxxxxxx [EnergyPlus_Support]" <EnergyPlus_Support@xxxxxxxxxxxxxxx> wrote:
 
I am using EMS to raise zone temperatures. I  get the following error upon running the simulation. How can this error be removed. 

** Severe  ** DualSetPointWithDeadBand: Effective heating set-point higher than effective cooling set-point - increase deadband if using unmixed air model
   **   ~~~   ** occurs in Zone=OFFICE During Warmup & Sizing, Environment=WASHINGTON DC REAGAN AP ANN HTG 99.6% CONDNS DB, at Simulation time=01/21 00:00 - 00:01
   **   ~~~   ** LoadToHeatingSetPoint=-8217.848, LoadToCoolingSetPoint=-118730.832
   **   ~~~   ** Zone TempDepZnLd=337.00
   **   ~~~   ** Zone TempIndZnLd=6493.26
   **   ~~~   ** Zone Heating ThermostatSetPoint=21.00
   **   ~~~   ** Zone Cooling ThermostatSetPoint=0.00




__._,_.___

Posted by: Jean Marais <jeannieboef@xxxxxxxxx>


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Visit Your Group
Yahoo! Groups
• Privacy • Unsubscribe • Terms of Use

__,_._,___