The heating setpoint (HtgSP) is greater than the cooling setpoint (ClgSP). For example, your HtgSP and ClgSP are 20 and 21 respectively (deadband = 1 C), then in your EMS you change to HtgSP = 22 --> error. You must also raise your ClgSP so that it is bigger than the HtgSP. The restriction prohibits sinultanious heating and cooling.
ÂI am using EMS to raise zone temperatures. I  get the following error upon running the simulation. How can this error be removed.Â** Severe  ** DualSetPointWithDeadBand: Effective heating set-point higher than effective cooling set-point - increase deadband if using unmixed air model  **  ~~~  ** occurs in Zone=OFFICE During Warmup & Sizing, Environment=WASHINGTON DC REAGAN AP ANN HTG 99.6% CONDNS DB, at Simulation time=01/21 00:00 - 00:01  **  ~~~  ** LoadToHeatingSetPoint=-8217.848, LoadToCoolingSetPoint=-118730.832  **  ~~~  ** Zone TempDepZnLd=337.00  **  ~~~  ** Zone TempIndZnLd=6493.26  **  ~~~  ** Zone Heating ThermostatSetPoint=21.00  **  ~~~  ** Zone Cooling ThermostatSetPoint=0.00