Re: [EnergyPlus_Support] Error message





The heating setpoint (HtgSP) is greater than the cooling setpoint (ClgSP). For example, your HtgSP and ClgSP are 20 and 21 respectively (deadband = 1 C), then in your EMS you change to HtgSP = 22 --> error. You must also raise your ClgSP so that it is bigger than the HtgSP. The restriction prohibits sinultanious heating and cooling.

On 25 Feb 2016 9:12 pm, "Fakeha Sehar fakeha_s@xxxxxxxxx [EnergyPlus_Support]" <EnergyPlus_Support@xxxxxxxxxxxxxxx> wrote:
 

I am using EMS to raise zone temperatures. I  get the following error upon running the simulation. How can this error be removed. 

** Severe  ** DualSetPointWithDeadBand: Effective heating set-point higher than effective cooling set-point - increase deadband if using unmixed air model
   **   ~~~   ** occurs in Zone=OFFICE During Warmup & Sizing, Environment=WASHINGTON DC REAGAN AP ANN HTG 99.6% CONDNS DB, at Simulation time=01/21 00:00 - 00:01
   **   ~~~   ** LoadToHeatingSetPoint=-8217.848, LoadToCoolingSetPoint=-118730.832
   **   ~~~   ** Zone TempDepZnLd=337.00
   **   ~~~   ** Zone TempIndZnLd=6493.26
   **   ~~~   ** Zone Heating ThermostatSetPoint=21.00
   **   ~~~   ** Zone Cooling ThermostatSetPoint=0.00



__._,_.___

Posted by: Jean Marais <jeannieboef@xxxxxxxxx>


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Visit Your Group
Yahoo! Groups
PrivacyUnsubscribeTerms of Use

__,_._,___