[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]

RE: [EnergyPlus_Support] Fan coil question





I have never seen an AirLoop object listed in the zone equipment list. If AirLoopHVAC:UnitarySystem can function as a zone equipment (listed in the list) that would be very interesting and very new to me. Time to ask the helpdesk I'd say. Keep us posted.
Jean

On 11 Apr 2016 2:45 pm, "'Jones, Christopher' Christopher.r.Jones@xxxxxxxxxxxx [EnergyPlus_Support]" <EnergyPlus_Support@xxxxxxxxxxxxxxx> wrote:
 

Thanks for that hint.

 

I donâ??t completely understand the use of the AirLoopHVAC:UnitarySystem object. You note ZoneHVAC:UnitarySystem but the IO Reference doesnâ??t specifically include that object. In the AirLoopHVAC:UnitarySystem description, it states that this object can be modeled as zone equipment (i.e., listed in a ZoneHVAC:EquipmentList). This leaves me wondering exactly how it would be defined in an example.

 

I grepped the ExampleFiles folder and didnâ??t find an example of ZoneHVAC:UnitarySystem in any of those files.

 

 

 

 

cid:image003.png@01D09C46.E75BA0D0

Christopher Jones, P.Eng.
Senior Engineer

 

WSP Canada Inc.

2300 Yonge Street, Suite 2300

Toronto, ON M4P 1E4
T +1 416-644-4226

F +1 416-487-9766

C +1 416-697-0056

 

www.wspgroup.com

 

From: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx]
Sent: Sunday, April 10, 2016 6:01 PM
To: EnergyPlus_Support@xxxxxxxxxxxxxxx
Subject: Re: [EnergyPlus_Support] Fan coil question

 

 

Jim's suggestion would work.

 

There's a ZoneHVAC:UnitarySystem that would do the job here as well: it accepts a cooling coil, a heating coil and a supplementary heating coil as far as I recall.

 



Envoyé de mon iPhone


Le 7 avr. 2016 à 20:20, "Jean Marais jeannieboef@xxxxxxxxx [EnergyPlus_Support]" <EnergyPlus_Support@xxxxxxxxxxxxxxx> a écrit :

 

Perhaps in newer versions...in the past I would implement a unitary system (which is not a zone equipment, but you could imagine it as such) which can have water or dx cooling + water or dx or electric heating. The catch is you can only have one unit (airloop) per zone, where as with zone equipment there is no limit.

On 7 Apr 2016 4:08 pm, "'Jones, Christopher' Christopher.r.Jones@xxxxxxxxxxxx [EnergyPlus_Support]" <EnergyPlus_Support@xxxxxxxxxxxxxxx> wrote:

 

We see many high rise multi-family buildings with 2-pipe fan coils and a backup electric heating coil for shoulder seasons when the system is in cooling mode. Can this type of arrangement be modeled with EnergyPlus?

 

 

<image001.png>

Christopher Jones, P.Eng.
Senior Engineer

 

WSP Canada Inc.

2300 Yonge Street, Suite 2300

Toronto, ON M4P 1E4
T +1 416-644-4226

F +1 416-487-9766

C +1 416-697-0056

 

www.wspgroup.com

 



You are receiving this communication because you are listed as a current WSP contact. Should you have any questions regarding WSPâ??s electronic communications policy, please consult our Anti-Spam Commitment www.wspgroup.com/casl. For any concern or if you believe you should not be receiving this message, please forward this message to us at caslcompliance@xxxxxxxxxxxx so that we can promptly address your request. This message is intended only for the use of the individual or entity to which it is addressed, and may contain information which is privileged, confidential, proprietary or exempt from disclosure under applicable law. If you are not the intended recipient or the person responsible for delivering the message to the intended recipient, you are strictly prohibited from disclosing, distributing, copying or in any way using this message. If you have received this communication in error, please notify the sender, and destroy and delete any copies you may have received.

WSP provides professional land surveying services through the following entities: WSP Surveys (AB) Limited Partnership and WSP Surveys (BC) Limited Partnership



You are receiving this communication because you are listed as a current WSP contact. Should you have any questions regarding WSPâ??s electronic communications policy, please consult our Anti-Spam Commitment www.wspgroup.com/casl. For any concern or if you believe you should not be receiving this message, please forward this message to us at caslcompliance@xxxxxxxxxxxx so that we can promptly address your request. This message is intended only for the use of the individual or entity to which it is addressed, and may contain information which is privileged, confidential, proprietary or exempt from disclosure under applicable law. If you are not the intended recipient or the person responsible for delivering the message to the intended recipient, you are strictly prohibited from disclosing, distributing, copying or in any way using this message. If you have received this communication in error, please notify the sender, and destroy and delete any copies you may have received.

WSP provides professional land surveying services through the following entities: WSP Surveys (AB) Limited Partnership and WSP Surveys (BC) Limited Partnership



__._,_.___

Posted by: Jean Marais <jeannieboef@xxxxxxxxx>


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Visit Your Group
Yahoo! Groups
• Privacy • Unsubscribe • Terms of Use

__,_._,___