If you are reporting the load (demand) each second and want the GJ per hour then take the average of the 3,600 loads each second, divide by 1000 to get kWh then
covert to GJ ( * 0.0036). But that is the load for the zone and does not equate to the energy used to meet the load. Christopher Jones,
P.Eng.
WSP Canada Inc. 2300 Yonge Street, Suite 2300 Toronto, ON M4P 1E4 F +1 416-487-9766 C +1 416-697-0056 From: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx]
Dear All, I calculated the following by using ILAS for 1 year. Report: HVAC Sizing Summary For: Entire Facility Zone Cooling
Here, Calculated Design Cooling Load [W]=
39246.61 W .. is this calculation for per second ??? and if I want to convert this to
GJ per Hour how can I do this?? Thank you.
Best Wishes,
Sajal Chowdhury
__._,_.___ Posted by: "Jones, Christopher" <Christopher.r.Jones@xxxxxxxxxxxx> EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The EnergyPlus web site is found at: http://www.energyplus.net/ The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button. __,_._,___ |