Re: [EnergyPlus_Support] Chiller:Electric- Sizing Factor value less than 1
Rajeev,
I did not look at the file you reference, however I think this is the rationale:
* When more than one chiller is present in a chilled water plant ANDÂ
* you autosize the chillers ANDÂ
* the sizing factor is blank or 1.0,Â
* E+ assigned 100% of the peak load to EACH chiller
If you have two chillers and want each to serve 50% of the load, you should set the sizing factor = 0.5
Similarly, if there are 3 chillers, you might set the sizing factor = 0.4
p.s., this is also true for boilers
On Sun, Jul 3, 2016 at 6:49 PM, <mailto:rajeevkamal@xxxxxxxxx>rajeevkamal@xxxxxxxxx [EnergyPlus_Support] <<mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx>EnergyPlus_Support@xxxxxxxxxxxxxxx> wrote:
> Â
> I wanted to understand the use of sizing factor for mechanical equipment in a specific case.Â
> For cooling and heating a range of 1 and more make sense to overcome unexpected demands.Â
>
>
> However, on review of the idf RefBldgLargeOfficeNew2004_v1.4_8.5_5A_USA_IL_CHICAGO-OHARE.idf, The sizing factors used for chillers are set to 0.4.Â
> In what situation is this a good idea for sizing the chillers?
>
>
> Regards
> Rajeev
> Â
>
--
James V Dirkes II, PE, BEMP, LEED AP
CEO/President
The Building Performance Team Inc.
1631 Acacia Dr, GR, Mi 49504
Direct: 616.450.8653
<mailto:jim@xxxxxxxxxxxxxxxxxxxxxxxxxxx>jim@xxxxxxxxxxxxxxxxxxxxxxxxxxx
<http://buildingperformanceteam.com>Website l  <https://www.linkedin.com/pub/jim-dirkes/7/444/413>LinkedIn | <http://buildingperformanceteam.com/bpt-insights-blog/item/73-modeled-performance-isn-t-actual-performance>May 2016 ASHRAE Journal article on energy modeling
<p style="margin-bottom:6.0pt;text-autospace:none"><span style="font-size:10pt;font-family:Calibri,sans-serif;background-image:initial;background-position:initial;background-repeat:initial">Either I win ? or I learn. </span><br></p>
__._,_.___
Posted by: Jim Dirkes <jim@xxxxxxxxxxxxxxxxxxxxxxxxxxx>
EnergyPlus support is found at:
<http://energyplus.helpserve.com>http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx
The EnergyPlus web site is found at:
<http://www.energyplus.net/>http://www.energyplus.net/
The group web site is:
<http://groups.yahoo.com/group/EnergyPlus_Support/>http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
<http://geo.yahoo.com/serv?s=97476590/grpId=3387488/grpspId=1705007389/msgId=36635/stime=1467591865>
<https://groups.yahoo.com/neo/groups/EnergyPlus_Support/info;_ylc=X3oDMTJlOHFvMjg1BF9TAzk3MzU5NzE0BGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwN2dGwEc2xrA3ZnaHAEc3RpbWUDMTQ2NzU5MTg2NQ-->Visit Your Group
* <https://groups.yahoo.com/neo/groups/EnergyPlus_Support/members/all;_ylc=X3oDMTJmOGJza2NoBF9TAzk3MzU5NzE0BGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwN2dGwEc2xrA3ZtYnJzBHN0aW1lAzE0Njc1OTE4NjU->New Members 8
<https://groups.yahoo.com/neo;_ylc=X3oDMTJkZ2ZkaHRsBF9TAzk3NDc2NTkwBGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwNmdHIEc2xrA2dmcARzdGltZQMxNDY3NTkxODY1><http://l.yimg.com/ru/static/images/yg/img/email/new_logo/logo-groups-137x15.png>
? <https://info.yahoo.com/privacy/us/yahoo/groups/details.html>Privacy ? <mailto:EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx?subject=Unsubscribe>Unsubscribe ? <https://info.yahoo.com/legal/us/yahoo/utos/terms/>Terms of Use
__,_._,___