RE: [EnergyPlus_Support] Problem with AirflowNetwork





Lixing Gu,

thanks for your answer!

What else found strange for me was the fact that a colleague model, like mine, have not shown this warning...

I'll find more information aboute the Airflow Network Model, for better understanding.

Thanks a lot!

Paulo Roberto. 



De: "Lixing Gu gu@xxxxxxxxxxxx [EnergyPlus_Support]" <EnergyPlus_Support@xxxxxxxxxxxxxxx>
Enviada: 2016/11/01 11:12:15
Para: EnergyPlus_Support@xxxxxxxxxxxxxxx
Assunto: RE: [EnergyPlus_Support] Problem with AirflowNetwork
 
 

 

Paulo:

 

The warning messages are informative. When the SurfaceAverageCalculation choice is entered, the model can generate wind pressure coefficients for 4 vertical exterior orientations and 1 horizontal roof. It is better to follow suggestions. If your intent is to use 2 exterior surfaces, you may ignore warning messages.

 

Hope this helps.

 

Lixing Gu

 

From: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx]
Sent: Monday, October 31, 2016 11:02 PM
To: EnergyPlus_Support@yahoogroups.c om
Subject: [EnergyPlus_Support] Problem with AirflowNetwork

 



Hello, everybody!

I'm simulating a 4 zones model (two on the ground, one on the side and one above the first two) using the EnergyPlus model of natural ventilation.

I have reviewed the model in the SketchUp and DXF file. It's OK, but I am getting the following warnings:

Program Version,EnergyPlus, Version 8.4.0-832e4bb9cb, YMD=2016.11.01 00:36,IDD_Version 8.4.0
   ** Warning ** GetAirflowNetworkInput: SurfaceAverageCalculation is entered for field = Wind Pressure Coefficient Type, but no roof surface is defined using an AirflowNetwork:MultiZone:Surface object.
   **   ~~~   ** Reconsider if this is your modeling intent. Simulation continues.
   ** Warning ** GetAirflowNetworkInput: SurfaceAverageCalculation is entered for field = Wind Pressure Coeffi cient Type.
   **   ~~~   ** The AirflowNetwork model provides wind pressure coefficients for 4 vertical exterior orientations and 1 horizontal roof.
   **   ~~~   **  There are only 2 exterior surface orientations defined in this input file using AirflowNetwork:MultiZone:Surface objects.
   **   ~~~   ** Reconsider if this is your modeling intent. Simulation continues.
   ************* Testing Individual Branch Integrity
   ************* All Branches passed integrity testing
   ************* Testing Individual Supply Air Path Integrity
   ************* All Supply Air Paths passed integrity testing
   ************* Testing Individual Return Air Path Integrity
   ************* All Return Air Paths passed integrity testing
   ************* No node connection errors were found.
   ************* Beginning Simula tion
   ************* Simulation Error Summary *************
   ************* EnergyPlus Warmup Error Summary. During Warmup: 0 Warning; 0 Severe Errors.
   ************* EnergyPlus Sizing Error Summary. During Sizing: 0 Warning; 0 Severe Errors.
   ************* EnergyPlus Completed Successfully-- 3 Warning; 0 Severe Errors; Elapsed Time=00hr 00min 18.47sec

Could someone explain to me what this is and which is the possible cause of the problem?

Thanks for regards,

Paulo Roberto.





 


 



__._,_.___

Posted by: prln@xxxxxxxxxx


EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The EnergyPlus web site is found at:
http://www.energyplus.net/

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the &quot;search&quot; button.




Visit Your Group
Yahoo! Groups
• Privacy • Unsubscribe • Terms of Use

__,_._,___