This should be pretty easy. Read up on the LoadProfile:Plant object in
the documentation. You don't have to model a building so you could just
take the example file PipingSystem_Underground_TwoPipe and change the
loads and flow fraction schedules to match your plant (with other
modifications as you see fit). This "example" is not necessarily real
since users would typically use the Schedule:File object to read the
loads and flow fractions from a file. See example file 5ZoneTDV to see
how to read an external file.
From PipingSystem_Underground_TwoPipe:
LoadProfile:Plant,
Load Profile, !- Name
Plant Demand Inlet Node, !- Inlet Node Name
Plant Demand Outlet Node,!- Outlet Node Name
LoadSchedule, !- Load Schedule Name
0.004, !- Peak Flow Rate {m3/s}
FlowFracSchedule; !- Flow Rate Fraction Schedule Name
Schedule:Compact,
LoadSchedule, !- Name
Any Number, !- Schedule Type Limits Name
Through: 04/30, !- Field 1
For: AllDays, !- Field 2
Until: 24:00,2000, !- Field 3
Through: 09/30, !- Field 5
For: AllDays, !- Field 6
Until: 24:00,-3000, !- Field 7
Through: 12/31, !- Field 9
For: AllDays, !- Field 10
Until: 24:00,2000; !- Field 11
Schedule:Compact,
FlowFracSchedule, !- Name
Any Number, !- Schedule Type Limits Name
Through: 12/31, !- Field 1
For: AllDays, !- Field 2
Until: 24:00,1; !- Field 3
From 5ZoneTDV:
Schedule:File,
natgasTDVfromCZ06com, !- Name
Any Number, !- Schedule Type Limits Name
..\datasets\TDV\TDV_2008_kBtu_CTZ06.csv, !- File Name <<<<- look
in this E+ folder for this file
3, !- Column Number
4; !- Rows to Skip at Top
------------------------------------
Posted by: Richard Raustad <rraustad@xxxxxxxxxxxx>
------------------------------------
EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx
The EnergyPlus web site is found at:
http://www.energyplus.net/
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
------------------------------------
Yahoo Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo Groups is subject to:
https://info.yahoo.com/legal/us/yahoo/utos/terms/