Francesco,
I always need to double-check whether I have properly assigned the "Source" and "Use" nodes properly. I'm not able to review the object definition now, but it appears that you might have those backwards (Source defined as Use).

Also, I wonder:

On Fri, Mar 10, 2017 at 3:04 AM, fpasserini.tn@xxxxxxxxx [EnergyPlus_Support] <EnergyPlus_Support@xxxxxxxxxxxxxxx> wrote:
 

I have tried but I got the following error:

**  Fatal  ** CalcDoe2DXCoil: Coil:WaterHeating:AirToWaterHeatPump:Pumped="AUX HW LOOP HP WATER HEATER HP WATER HEATING COIL" - Rated total cooling capacity is zero or less.
   ...Summary of Errors that led to program termination:
   ..... Reference severe error count=0
   ..... Last severe error=




--

James V Dirkes II, PE, BEMP, LEED AP
CEO/President
The Building Performance Team Inc.
1631 Acacia Dr, GR, Mi 49504

Direct / Mobile: 616.450.8653
jim@xxxxxxxxxxxxxxxxxxxxxxxxxxx

Website l  LinkedIn

Coffee cup conversation: Our friends, our company, our culture, our country, ourselves are not renewed once and for all. They are renewed every day.



__._,_.___

Posted by: Jim Dirkes <jim@xxxxxxxxxxxxxxxxxxxxxxxxxxx>


EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The EnergyPlus web site is found at:
http://www.energyplus.net/

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the &quot;search&quot; button.




Visit Your Group
Yahoo! Groups
• Privacy • Unsubscribe • Terms of Use

__,_._,___