Dear All,

We are investigating zone cooling load peak component summary for analyzing load contribution from all the internal and external sources (refer following table). We are struggling to answer few questions which are as follows:
  • We referred engineering manual and I/O guide to understand the sensible delayed column. We found delayed effect contribution is significant, sometime its higher than sensible instant. We are unable to clearly understand how this delayed effect could contribute so high compared to instant gain? what is the basis of this delayed calculations?
  • The reported value of sensible delayed could be minimize to zero if Radiative heat fraction defined for people, lights and equipment are reduced to zero in IDF. Hence, Radiative heat fraction effects sensible delayed effect significantly. Are there any industry standard to use optimum Radiative heat fraction for the people, lights and equipment? 
  • If the building is highly insulated, the sensible delayed for people, lights and equipment are reported with (-ve sign convention). In the following table the external and interzone wall showing gains with -ve sign. What does -ve sign indicates in sensible delayed column? How to interpret this correctly?

Estimated Cooling Peak Load Components


Sensible - Instant [W]Sensible - Delayed [W]Sensible - Return Air [W]Latent [W]Total [W]%Grand Total
People4396.356572.28 4711.6815680.3137.55
Lights869.223686.380.00 4555.5910.91
Equipment13153.0311493.52 0.0024646.5559.01
Refrigeration0.00 0.000.000.000.00
Water Use Equipment0.00  0.000.000.00
HVAC Equipment Losses0.000.00  0.000.00
Power Generation Equipment0.000.00  0.000.00
Infiltration863.78  974.581838.374.40
Zone Ventilation0.00  0.000.000.00
Interzone Mixing0.00  0.000.000.00
Roof 25.86  25.860.06
Interzone Ceiling 0.00  0.000.00
Other Roof 0.00  0.000.00
Exterior Wall -4824.8  -4824.8-11.6
Interzone Wall -2594.2  -2594.2-6.2
Ground Contact Wall 0.00  0.000.00
Other Wall 0.00  0.000.00
Exterior Floor -580.3  -580.3-1.4
Interzone Floor 0.00  0.000.00
Ground Contact Floor 0.00  0.000.00
Other Floor 0.00  0.000.00
Fenestration Conduction1790.84   1790.844.29
Fenestration Solar 1225.17  1225.172.93
Opaque Door 0.00  0.000.00
Grand Total21073.2215003.940.005686.2741763.43



â??We would appreciate any help on this.

Thanks, â??

--


Javed Iqbal, LEED AP, CEA
Sr. Energy Analyst 







__._,_.___

Posted by: Javed Iqbal <eee.javed@xxxxxxxxx>


EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The EnergyPlus web site is found at:
http://www.energyplus.net/

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the &quot;search&quot; button.




Visit Your Group
Yahoo! Groups
PrivacyUnsubscribeTerms of Use

__,_._,___