[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]

Re: [EnergyPlus_Support] Re: CentralHeatPumpSystem with one chiller/heater [2 Attachments]





Hello, Jim
The source/condenser temperature is constant because the PlantComponent:TemperatureSource object is used.
The calculated output is constant. I have recalculate the output in excel, considering the parameters used for the curve, and the polynomial formula is calculated by EnergyPlus properly.  
The strange issue is that the leaving chilled water temperature used in the calculation is not taken from the dynamic simulation but it is the â??Reference Cooling Mode Leaving Chilled Water Temperatureâ??.
I have plotted the â??Cooling Mode Electric Input to Cooling Output Ratio Function of Temperatureâ?? (CHILLERHEATERCLGEIRFT) too and Iâ??m attaching it now. As for that curve, the temperature 6°C, which is the setpoint manager temperature, is considered as leaving chilled water temperature!?
As you can see in the second picture, the chiller-heater is working in cooling mode only one hour. Therefore the setpoint manager temperature is not met.
Best Regards



__._,_.___
View attachments on the web

Posted by: fpasserini.tn@xxxxxxxxx


EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The EnergyPlus web site is found at:
http://www.energyplus.net/

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Visit Your Group
Yahoo! Groups
• Privacy • Unsubscribe • Terms of Use

__,_._,___
Attachment Converted: "D:\Eudora\Attach\Cattura3.JPG" Attachment Converted: "D:\Eudora\Attach\img2.JPG"