[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]

Re: [EnergyPlus_Support] Re: CentralHeatPumpSystem with one chiller/heater





"Properly" should mean that E+ is using the â??actual chilled water temp and actual condenser water temp. Is that the case? 
It's using the "Performance Curve Input Variable 1 Value", the "Performance Curve Input Variable 2 Value" and the parameters defined in the curve to calculate the "Performance Curve Output Value". The problem is that it is not using the correct value of "Performance Curve Input Variable 1 Value", in my opinion. So, wrong input -> wrong output (sorry, I was not clear).
Is the setpoint manager value different than the "reference" temperature?â??
Yes, 
â??Reference Cooling Mode Leaving Chilled Water Temperatureâ?? = 6.7°C
setpoint manager temperature = 6°C
for CHILLERHEATERCLGCAPFT it's using 6.7°C
for CHILLERHEATERCLGEIRFT it's using 6.0°C
In both cases I would expect the temperature from the dynamic simulation, which is higher (15-16°C), because the system is not working properly.
You'll need to determine why the chiller does not operate for more than one hour. That may â??be part of the reason for the curve output problem.
Ok. Actually I was thinking in the other way: the chiller/heater doesn't operate properly, is the problem relative to the curves (or to the points of the curves where the system is operating)?


---In EnergyPlus_Support@xxxxxxxxxxxxxxx, <jim@...> wrote :

Francesco,
Comments below...

On Mon, Jul 3, 2017 at 8:46 AM, fpasserini.tn@... [EnergyPlus_Support] <EnergyPlus_Support@xxxxxxxxxxxxxxx> wrote:
 

Hello, Jim
The source/condenser temperature is constant because the PlantComponent: TemperatureSource object is used.
The calculated output is constant. I have recalculate the output in excel, considering the parameters used for the curve, and the polynomial formula is calculated by EnergyPlus properly.  
â??"Properly" should mean that E+ is using the â??actual chilled water temp and actual condenser water temp. Is that the case? 
The strange issue is that the leaving chilled water temperature used in the calculation is not taken from the dynamic simulation but it is the â??Reference Cooling Mode Leaving Chilled Water Temperatureâ??.
â?? Is the setpoint manager value different than the "reference" temperature?â??
I have plotted the â??Cooling Mode Electric Input to Cooling Output Ratio Function of Temperatureâ?? (CHILLERHEATERCLGEIRFT) too and Iâ??m attaching it now. As for that curve, the temperature 6°C, which is the setpoint manager temperature, is considered as leaving chilled water temperature!?
As you can see in the second picture, the chiller-heater is working in cooling mode only one hour. Therefore the setpoint manager temperature is not met.
â?? You'll need to determine why the chiller does not operate for more than one hour. That may â??be part of the reason for the curve output problem.
Best Regards




--

James V Dirkes II, CEO / President
The Building Performance Team Inc.
1631 Acacia Dr, GR, MI 49504

(alphabet soup of efforts for excellence: PE, BEMP, BCxP, LEED AP)

Direct / Mobile: 616.450.8653
jim@...

Website l  LinkedIn

Coffee conversation: They love truth when it enlightens them, they hate truth when it accuses them? They love truth when it reveeals itself, and hate it when it reveals them.

.

 


__._,_.___

Posted by: fpasserini.tn@xxxxxxxxx


EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The EnergyPlus web site is found at:
http://www.energyplus.net/

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the &quot;search&quot; button.




Visit Your Group
Yahoo! Groups
• Privacy • Unsubscribe • Terms of Use

__,_._,___