[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]

Re: [EnergyPlus_Support] Efficiency for AC equipment in EnergyPlus





Thanks a lot!

best,
William

On Tue, Aug 8, 2017 at 1:28 AM, Julien Marrec julien.marrec@xxxxxxxxx [EnergyPlus_Support] <EnergyPlus_Support@xxxxxxxxxxxxxxx> wrote:
 

Wenliang,

At the top of every DOE prototype IDF file, there's a comment section (each line starts with '!'). It expains a bit how the model is articulated, included the type of HVAC system used. That should be helpful for you.

For eexample, here's an extract of the `RefBldgLargeHotelNew2004_Chicago.idf`

! HVAC:         2 air-cooled electric chillers, natural gas boiler, VAV in common areas, elec. unit heater in top floor corridor
!               Dedicated OA system and 4-pipe fan coil units in guest rooms
!               Economizer per 90.1-2004 for VAV system
!               Chiller part load curve corrected from original

[...]

! Zonal Equipment:                ZoneHVAC:FourPipeFanCoil, ZoneHVAC:UnitHeater (top floor corridor)
! Air Primary Loops:              VAV with Reheat, DOAS
! Plant Loops:                    SHWSys1, HeatSys1, CoolSys1
! System Equipment Autosize:      Yes
! Purchased Cooling:              None
! Purchased Heating:              None
! Coils:                          Coil:Cooling:Water, Coil:Heating:Water, Coil:Heating:Electric
! Pumps:                          Yes
! Boilers:                        Boiler:HotWater (gas-fired)
! Chillers:                       Chiller:Electric:EIR (air-cooled)


As you can see above, you might be interested in searching for Chiller:Electric:EIR. You'll find two: CoolSys1 Chiller 1 and CoolSys1 Chiller 2, both with have a cooling cop of 5.5

  Chiller:Electric:EIR,
    CoolSys1 Chiller 2,      !- Name
    AUTOSIZE,                !- Reference Capacity {W}
    5.5,                     !- Reference COP {W/W}
    [...]


Best,
Julien




--
Julien Marrec, EBCP, BPI MFBA
Owner at EffiBEM
T: +33 6 95 14 42 13

LinkedIn (en) | (fr) :

2017-08-08 3:19 GMT+02:00 william Lee liwenliang1984@xxxxxxxxx [EnergyPlus_Support] <EnergyPlus_Support@yahoogroups.com>:
 

I got the reference model (large hotel) from DOE website, they do have COP there, but no value, it looks like this building is using other HVAC system instead of DX Coil or Chiller you mentioned.

best,
Wenliang

On Mon, Aug 7, 2017 at 5:05 PM, Jim Dirkes jim@xxxxxxxxxxxxxxxxxxxxxxxxxxm [EnergyPlus_Support] <EnergyPlus_Support@yahoogroups.com> wrote:
 

What files do not show a COP? (since both of the screen captures you included have COP)

On Mon, Aug 7, 2017 at 3:50 PM, william Lee liwenliang1984@xxxxxxxxx [EnergyPlus_Support] <EnergyPlus_Support@yahoogroups.com> wrote:
 

Hi, James,

For some buildings, I didn't find either Coil or Chiller for efficiency, is there some thing wrong here, I used the reference model from DOE.
Inline image 1Inline image 2

On Mon, Aug 7, 2017 at 1:27 PM, Jim Dirkes jim@xxxxxxxxxxxxxxxxxxxxxxxxxxm [EnergyPlus_Support] <EnergyPlus_Support@yahoogroups.com> wrote:
 

William,
For a DX coil, have you seen this? (COP is a measure of efficiency)
Inline image 1

For a Chiller, it's in the Chiller object
Inline image 2

On Mon, Aug 7, 2017 at 2:16 PM, liwenliang1984@xxxxxxxxx [EnergyPlus_Support] <EnergyPlus_Support@yahoogroups.com> wrote:
 

Hi all,


       I am just wondering how can I set up efficiency for AC equipment in EnergyPlus, I looked around almost all the parameters in EnergyPlus, I didn't find the parameter for AC efficiency.

Thanks!

William




--

James V Dirkes II, CEO / President
The Building Performance Team Inc.
1631 Acacia Dr, GR, MI 49504

(alphabet soup of efforts for excellence: PE, BEMP, BCxP, LEED AP)

Direct / Mobile: 616.450.8653
jim@xxxxxxxxxxxxxxxxxxxxxxxxxxm

Website l  LinkedIn

Coffee conversation: What spirit is so empty and blind, that it cannot recognize the fact that the foot is more noble than the shoe, and skin more beautiful than the garment with which it is clothed?





--

James V Dirkes II, CEO / President
The Building Performance Team Inc.
1631 Acacia Dr, GR, MI 49504

(alphabet soup of efforts for excellence: PE, BEMP, BCxP, LEED AP)

Direct / Mobile: 616.450.8653
jim@xxxxxxxxxxxxxxxxxxxxxxxxxxm

Website l  LinkedIn

Coffee conversation: What spirit is so empty and blind, that it cannot recognize the fact that the foot is more noble than the shoe, and skin more beautiful than the garment with which it is clothed?






__._,_.___

Posted by: william Lee <liwenliang1984@xxxxxxxxx>


EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The EnergyPlus web site is found at:
http://www.energyplus.net/

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the &quot;search&quot; button.




Visit Your Group
Yahoo! Groups
• Privacy • Unsubscribe • Terms of Use

__,_._,___