[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]

Re: [EnergyPlus_Support] Control of AirTerminal:SingleDuct:VAV:Reheat - Sizing Problem





That is as per G3.1.2.9.1,  sized supply-air-to-room-air temperature difference of  20degF (11.1degC) . All the Spaces winter set-point is 21degC so central heating design supply air tempretaire is 32.1 degC.


On Thu, Mar 15, 2018 at 4:55 PM, Germán Campos ecoeficiente@xxxxxxxxx [EnergyPlus_Support] <EnergyPlus_Support@xxxxxxxxxxxxxxx> wrote:
 

Which are heating design supply temperatures in system and zone sizing?


____________________

Germán Campos
Aurea Consulting  
www.ecoeficiente.es

2018-03-15 11:53 GMT+01:00 Javed Iqbal eee.javed@xxxxxxxxx [EnergyPlus_Support] <EnergyPlus_Support@yahoogroups.com>:
 

Dear All,

I assigned a typical VAV system (Baseline System 5) with reheat but there are many heating unmet hours in the zones served by the system. I did most of the quality checks (correct OA, zone setpoints, zone and system sizing etc.) to see where the problem lies. And i found ' AirTerminal:SingleDuct:VAV:Reheat' is NOT active or sizing is zero in HTML report. To further ascertain the cause of the problem, I plotted temperatures [ see attachment] at all the nodes to see the temperature regime. This also shows that reheat coil doesn't raise the air temperature to meet the room set-point.  

This is being simulated for CZ5A.

I also tried to look out for some solutions discussed here [ LINK LINK ] but unfortunately nothing works for me. 

I would appreciate any help in this regard.

Thank you,  

--


Javed Iqbal, LEED AP, CEA
Sr. Energy Analyst 









--


Javed Iqbal, LEED AP, CEA
Sr. Energy Analyst 







__._,_.___

Posted by: Javed Iqbal <eee.javed@xxxxxxxxx>


EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The EnergyPlus web site is found at:
http://www.energyplus.net/

The group web site is:
http://groups..yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the &quot;search&quot; button.




Visit Your Group
Yahoo! Groups
• Privacy • Unsubscribe • Terms of Use

__,_._,___