Hi
I know this problem well, but I can't open an idf right now to give you the exact solution, there is a something around the bottom of the object AirTerminal:SingleDuct:VAV:Reheat
which turns on and off the reheat coil. Sorry I can't be more precise right now fiddle around with this object and it will suddenly magically turn on
From: EnergyPlus_Support@xxxxxxxxxxxxxxx <EnergyPlus_Support@xxxxxxxxxxxxxxx> on behalf of Javed Iqbal eee.javed@xxxxxxxxx [EnergyPlus_Support]
<EnergyPlus_Support@xxxxxxxxxxxxxxx>
Sent: 15 March 2018 10:53 To: EnergyPlus_Support@xxxxxxxxxxxxxxx Subject: [EnergyPlus_Support] Control of AirTerminal:SingleDuct:VAV:Reheat - Sizing Problem [1 Attachment]
Dear All,
I assigned
a typical VAV system (Baseline System 5) with reheat but there are many heating unmet hours in the zones served by the system. I did most of the quality checks (correct OA, zone setpoints, zone and system sizing
etc.) to see where the problem lies. And i found '
AirTerminal:SingleDuct:VAV:Reheat' is
NOT active or sizing is zero in HTML report. To further ascertain the cause of the problem, I plotted
temperatures [ see attachment] at all the nodes to see the temperature regime. This also shows that reheat coil doesn't raise the air temperature to meet the room set-point.
This is being simulated for CZ5A.
I
also tried to look out for some solutions discussed here [
LINK LINK ]
but unfortunately nothing works for me.
I would appreciate any help in this regard.
Thank you,
Javed Iqbal, LEED AP, CEA
Sr. Energy Analyst
__._,_.___ Posted by: Annie Marston <anniemarston@xxxxxxxxxxx> EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The EnergyPlus web site is found at: http://www.energyplus.net/ The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button. __,_._,___ |