Re: [EnergyPlus_Support] Help for error message





If your cooling setpoint is 1 Degree C,  then are you trying to model some sort of fridge? 

You can't cool with your fan coil below the coldest air that it can blow in... 13 degrees C. 

On Mon, 30 Apr 2018, 13:44 aleck1314@xxxxxxxx [EnergyPlus_Support], <EnergyPlus_Support@xxxxxxxxxxxxxxx> wrote:
 

Hi EnergyPlus users,


I can't find the origin of the error in my model.


** Severe  ** InitPurchasedAir: For ZoneHVAC:IdealLoadsAirSystem = BU7 THERMAL ZONE IDEAL LOADS AIR SYSTEM serving Zone BU7 THERMAL ZONE

   **   ~~~   ** ..the minimum supply air temperature for cooling [13.00] is greater than the zone cooling mean air temperature (MAT) setpoint [1.00].


   *************  ** Severe  ** InitPurchasedAir: For ZoneHVAC:IdealLoadsAirSystem = BU7 THERMAL ZONE IDEAL LOADS AIR SYSTEM serving Zone BU7 THERMAL ZONE, the minimum supply air temperature for cooling error continues

   *************  **   ~~~   **   This error occurred 59738 total times;


Can someone help me?

Thanks in advance

Aleck



__._,_.___

Posted by: Jean Marais <jeannieboef@xxxxxxxxx>


EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The EnergyPlus web site is found at:
http://www.energyplus.net/

The group web site is:
http://groups..yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the &quot;search&quot; button.




Visit Your Group
Yahoo! Groups
• Privacy • Unsubscribe • Terms of Use

__,_._,___