The fan won't be variable in the furnace. From the Furnace.idf example 
file you see that the air flow rate will be 1.3 m3/s when heating is 
active if you use constant fan. If you use cycling fan then the air flow 
rate will be 1.3 m3/s when the furnace is on and 0 when it is off. This 
results in an average air flow rate over the simulation time step.

   AirLoopHVAC:Unitary:Furnace:HeatOnly,
     1.3,                     !- Heating Supply Air Flow Rate {m3/s}

Now if you put the fan on the main branch, and use water coils (example 
file is 5ZoneAirCooled.idf) or CoilSystem (5ZoneAutoDXVAV.idf), these 
also on the main branch. And then use VAV terminal units, then the fan 
will vary it's speed as the terminal unit damper modulates.

On 2018-07-15 14:06, Paul paulnee@xxxxxxxxxxxx [EnergyPlus_Support] 
wrote:
> Would some kind soul please enlighten me on how to control a
> Fan:VariableVolume. Preferably in conjunction with a
> AirLoopHVAC:Unitary:Furnace:HeatOnly and it's associated coil.
> 
> Thanks so much,
> 
> Paul
> 
> 
> 
> ------------------------------------
> Posted by: Paul <paulnee@xxxxxxxxxxxx>
> ------------------------------------
> 
> EnergyPlus support is found at:
> http://energyplus.helpserve.com or send a message to 
> energyplus-support@xxxxxxxx
> 
> The EnergyPlus web site is found at:
> http://www.energyplus.net/
> 
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
> 
> Attachments are currently allowed but be mindful that not everyone has
> a high speed connection.  Limit attachments to small files.
> 
> EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under
> the Documentation link and press the &quot;search&quot; button.
> ------------------------------------
> 
> Yahoo Groups Links
> 
> 
> 


------------------------------------
Posted by: rraustad <rraustad@xxxxxxxxxxxx>
------------------------------------

EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The EnergyPlus web site is found at:
http://www.energyplus.net/

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the &quot;search&quot; button.
------------------------------------

Yahoo Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo Groups is subject to:
    https://info.yahoo.com/legal/us/yahoo/utos/terms/