Oh yeah, you can only use Fan:OnOff or Fan:ConstantVolume in the heat 
only furnace.

On 2018-07-15 14:35, Jim Dirkes jim@xxxxxxxxxxxxxxxxxxxxxxxxxxx 
[EnergyPlus_Support] wrote:
> Paul,
> (From memory)
> You don’t control it per se. E+ assumes that the fan can operate at
> flow proportionate to the cooling or heating load, and applies lower
> power at the same time.
> The lower power is determined by the fan curve coefficients that you
> assign in the fan object.
> Some of the Unitary objects do not allow a variable volume fan - check
> the I/O Reference doc for the Unitary object to see if yours allows
> it.
> 
> On Sun, Jul 15, 2018 at 2:06 PM Paul paulnee@xxxxxxxxxxxx
> [EnergyPlus_Support] <EnergyPlus_Support@xxxxxxxxxxxxxxx> wrote:
> 
>> Would some kind soul please enlighten me on how to control a
>> Fan:VariableVolume. Preferably in conjunction with a
>> AirLoopHVAC:Unitary:Furnace:HeatOnly and it's associated coil.
>> 
>> Thanks so much,
>> 
>> Paul
>  --
> 
> James V Dirkes II, CEO / President
> The Building Performance Team Inc.
> 1631 Acacia Dr, Grand Rapids, MI 49504
> 
> (alphabet soup of efforts for greater understanding: PE, BEMP, BCxP,
> LEED AP)
> 
> Direct / Mobile: 616..450.8653
> jim@xxxxxxxxxxxxxxxxxxxxxxxxxxx
> 
> Website [1]l  LinkedIn [2]
> 
> _ _
> 
> COFFEE CONVERSATION:
> 
> "Community" is not community unless it makes moral demands on you.
> 
> 
> 
> Links:
> ------
> [1] http://buildingperformanceteam.com
> [2] https://www.linkedin.com/pub/jim-dirkes/7/444/413
> [3] http://groups.yahoo.com/group/EnergyPlus_Support/
> [4]
> https://groups.yahoo.com/neo/groups/EnergyPlus_Support/info;_ylc=X3oDMTJlamhwMG40BF9TAzk3MzU5NzE0BGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwN2dGwEc2xrA3ZnaHAEc3RpbWUDMTUzMTY3OTc3Mw--
> [5]
> https://groups.yahoo.com/neo/groups/EnergyPlus_Support/members/all;_ylc=X3oDMTJmZ2wzcGpuBF9TAzk3MzU5NzE0BGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwN2dGwEc2xrA3ZtYnJzBHN0aW1lAzE1MzE2Nzk3NzM-
> [6]
> https://groups.yahoo.com/neo;_ylc=X3oDMTJkaHU2NjQzBF9TAzk3NDc2NTkwBGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwNmdHIEc2xrA2dmcARzdGltZQMxNTMxNjc5Nzcz
> [7] https://info.yahoo.com/privacy/us/yahoo/groups/details.html
> [8] https://info.yahoo.com/legal/us/yahoo/utos/terms/


------------------------------------
Posted by: rraustad <rraustad@xxxxxxxxxxxx>
------------------------------------

EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The EnergyPlus web site is found at:
http://www.energyplus.net/

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the &quot;search&quot; button.
------------------------------------

Yahoo Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo Groups is subject to:
    https://info.yahoo.com/legal/us/yahoo/utos/terms/