Although this has been the standard procedure for defining the
heating design day, I question the underlying logic and think
that will lead to oversizing. If the building is unoccupied,
i.e., no occupants, no lights, no equipment, then why would it be
heated to standard operating levels? I understand combining all
the worst case conditions to get a design load, but not when those
worst case conditions tend to exclude some others from ever
occurring.
Joe
Joe Huang
White Box Technologies, Inc.
346 Rheem Blvd., Suite 205A
Moraga CA 94556
yjhuang@xxxxxxxxxxxxxxxxxxxxxxxx
http://weather.whiteboxtechnologies.com for simulation-ready weather data
(o) (925)388-0265
(c) (510)928-2683
"building energy simulations at your fingertips"
Whatever
you specify as applicable on a Winter DesignDay is
included.. Most designers calculate heating loads,
however, with zero lights (or maybe 5% for security
lights), zero equipment and zero people.
Most
of the time, this makes sense, e.g., a long holiday such
as Christmas or New Year, when everyone is gone and the
building is quiet and dark. the Schedules might look
something like:
| SCHEDULE:COMPACT |
|
| Sched_PeopleAssembly |
| Fraction |
|
| Through: 12/31 |
|
| For: Weekdays |
| Until:
8:00,0.00 |
| Until:
11:00,0.20 |
| Until:
18:00,0.80 |
| Until:
22:00,0.20 |
| Until:
23:00,0.10 |
| Until:
24:00,0.00 |
| For: Saturday |
| Until:
8:00,0.00 |
| Until:
11:00,0.20 |
| Until:
21:00,0.60 |
| Until:
22:00,0.80 |
| Until:
23:00,0.10 |
| Until:
24:00,0.00 |
| For: Sunday Holidays |
| Until:
8:00,0.00 |
| Until:
13:00,0.10 |
| Until:
22:00,0.70 |
| Until:
23:00,0.20 |
| Until:
24:00,0.00 |
| For: SummerDesignDay |
| Until:
8:00,0.00 |
| Until:
11:00,0.20 |
| Until:
18:00,0.80 |
| Until:
21:00,0.70 |
| Until:
22:00,0.80 |
| Until:
23:00,0.20 |
| Until:
24:00,0.00 |
| For: WinterDesignDay AllOtherDays |
| Until:
24:00,0.00 |
|
|
| SCHEDULE:COMPACT |
|
| Sched_LtgAssembly |
| Fraction |
|
| Through: 12/31 |
|
| For: Weekdays |
| Until:
6:00,0.05 |
| Until:
9:00,0.40 |
| Until:
22:00,0.75 |
| Until:
23:00,0.25 |
| Until:
24:00,0.05 |
| For: Saturday |
| Until:
7:00,0.05 |
| Until:
9:00,0.30 |
| Until:
23:00,0.50 |
| Until:
24:00,0.05 |
| For: Sunday Holidays |
| Until:
7:00,0.05 |
| Until:
12:00,0.30 |
| Until:
22:00,0.65 |
| Until:
24:00,0.05 |
| For: SummerDesignDay |
| Until:
6:00,0.05 |
| Until:
9:00,0.40 |
| Until:
22:00,0.75 |
| Until:
23:00,0.50 |
| Until:
24:00,0.05 |
| For: WinterDesignDay AllOtherDays |
| Until:
24:00,0.00 |
|
|
| SCHEDULE:COMPACT |
|
| Sched_PlugsAssembly |
| Fraction |
|
| Through: 12/31 |
|
| For: Weekdays |
| Until:
6:00,0.05 |
| Until:
9:00,0.40 |
| Until:
22:00,0.75 |
| Until:
23:00,0.25 |
| Until:
24:00,0.05 |
| For: Saturday |
| Until:
7:00,0.05 |
| Until:
9:00,0.30 |
| Until:
23:00,0.50 |
| Until:
24:00,0.05 |
| For: Sunday Holidays |
| Until:
7:00,0.05 |
| Until:
12:00,0.30 |
| Until:
22:00,0.65 |
| Until:
24:00,0.05 |
| For: SummerDesignDay |
| Until:
6:00,0.05 |
| Until:
9:00,0.40 |
| Until:
22:00,0.75 |
| Until:
23:00,0.50 |
| Until:
24:00,0.05 |
| For: WinterDesignDay AllOtherDays |
| Until:
24:00,0.00 |
__._,_.___
Posted by: Joe Huang <yjhuang@xxxxxxxxxxxxxxxxxxxxxxxx>
EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx
The EnergyPlus web site is found at:
http://www.energyplus.net/
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
__,_._,___
|