Re: [EnergyPlus_Support] HVAC sizing





An interesting discussion point. We oversize equipment to mitigate user complaints. Funny enough, even ASHRAE lets us oversize heating by a safety factor of 1.2 and cooling by 1.15. The manufacturers of equipment like chillers design their equipment with the 95 percentile for hours at a specific part-load relative to the full load design desired. Because people have been sizing fairly consistently for so long, the matching equipment have become more tailor-made for the real situation. 

The correct way to size would be to do a good energy simulation and parametrically swap out different equipments with real operating efficiency curves and converge on a best combination (as you can do easily in designbuilder now FYI) . I've yet to see a building owner pay for that. And as the space allocation for the physical equipment is determined at the earliest design stage, a simulation of this sort is not really helpful as to much is still in flux. Having too little space for equipment is a horror so i'm all for oversizing at the early stages. 

On 1 Aug 2018 4:09 am, "Joe Huang YJHuang@xxxxxxxxxxxxxxxxxxxxxxxx [EnergyPlus_Support]" <EnergyPlus_Support@xxxxxxxxxxxxxxx> wrote:
 

Although this has been the standard procedure for defining the heating design day,  I question the underlying logic and think that will lead to oversizing.  If the building is unoccupied, i.e., no occupants, no lights, no equipment, then why would it be heated to standard operating levels?   I understand combining all the worst case conditions to get a design load, but not when those worst case conditions tend to exclude some others from ever occurring.

Joe

Joe Huang
White Box Technologies, Inc.
346 Rheem Blvd., Suite 205A
Moraga CA 94556
yjhuang@xxxxxxxxxxxxxxxxxxxxxxxx
http://weather.whiteboxtechnologies.com for simulation-ready weather data
(o) (925)388-0265
(c) (510)928-2683
"building energy simulations at your fingertips"
On 7/31/2018 11:47 AM, Jim Dirkes jim@xxxxxxxxxxxxxxxxxxxxxxxxxxx [EnergyPlus_Support] wrote:
 
Whatever you specify as applicable on a Winter DesignDay is included.. Most designers calculate heating loads, however, with zero lights (or maybe 5% for security lights), zero equipment and zero people.

Most of the time, this makes sense, e.g., a long holiday such as Christmas or New Year, when everyone is gone and the building is quiet and dark.  the Schedules might look something like:

SCHEDULE:COMPACT
Sched_PeopleAssembly
Fraction
Through: 12/31
For: Weekdays
Until: 8:00,0.00
Until: 11:00,0.20
Until: 18:00,0.80
Until: 22:00,0.20
Until: 23:00,0.10
Until: 24:00,0.00
For: Saturday
Until: 8:00,0.00
Until: 11:00,0.20
Until: 21:00,0.60
Until: 22:00,0.80
Until: 23:00,0.10
Until: 24:00,0.00
For: Sunday Holidays
Until: 8:00,0.00
Until: 13:00,0.10
Until: 22:00,0.70
Until: 23:00,0.20
Until: 24:00,0.00
For: SummerDesignDay
Until: 8:00,0.00
Until: 11:00,0.20
Until: 18:00,0.80
Until: 21:00,0.70
Until: 22:00,0.80
Until: 23:00,0.20
Until: 24:00,0.00
For: WinterDesignDay AllOtherDays
Until: 24:00,0.00


SCHEDULE:COMPACT
Sched_LtgAssembly
Fraction
Through: 12/31
For: Weekdays
Until: 6:00,0.05
Until: 9:00,0.40
Until: 22:00,0.75
Until: 23:00,0.25
Until: 24:00,0.05
For: Saturday
Until: 7:00,0.05
Until: 9:00,0.30
Until: 23:00,0.50
Until: 24:00,0.05
For: Sunday Holidays
Until: 7:00,0.05
Until: 12:00,0.30
Until: 22:00,0.65
Until: 24:00,0.05
For: SummerDesignDay
Until: 6:00,0.05
Until: 9:00,0.40
Until: 22:00,0.75
Until: 23:00,0.50
Until: 24:00,0.05
For: WinterDesignDay AllOtherDays
Until: 24:00,0.00


SCHEDULE:COMPACT
Sched_PlugsAssembly
Fraction
Through: 12/31
For: Weekdays
Until: 6:00,0.05
Until: 9:00,0.40
Until: 22:00,0.75
Until: 23:00,0.25
Until: 24:00,0.05
For: Saturday
Until: 7:00,0.05
Until: 9:00,0.30
Until: 23:00,0.50
Until: 24:00,0.05
For: Sunday Holidays
Until: 7:00,0.05
Until: 12:00,0.30
Until: 22:00,0.65
Until: 24:00,0.05
For: SummerDesignDay
Until: 6:00,0.05
Until: 9:00,0.40
Until: 22:00,0.75
Until: 23:00,0.50
Until: 24:00,0.05
For: WinterDesignDay AllOtherDays
Until: 24:00,0.00


On Tue, Jul 31, 2018 at 2:07 PM, my_sunny_night@xxxxxxxxx [EnergyPlus_Support] <EnergyPlus_Support@xxxxxxxxxxxxxxx> wrote:
 

Hello All,

Is the internal heat gain from occupants taken into account for heating equipment sizing?

Thanks




--

James V Dirkes II, CEO / President
The Building Performance Team Inc.
1631 Acacia Dr, Grand Rapids, MI 49504

(alphabet soup of efforts for greater understanding: PE, BEMP, BCxP, LEED AP)

Direct / Mobile: 616.450.8653
jim@xxxxxxxxxxxxxxxxxxxxxxxxxxx

Website l  LinkedIn

Coffee conversation:

A friend describes himself as â??mediocreâ??. In my estimation, heâ??s clearly amazing and exceptional, so it irritates me to hear him say that. Upon some reflection, I realize that he may be right.

Only one person in the world is the (literal) worldâ??s best. All of us can improve and should be actively improving. That means weâ??re all in the middle ? a mediocrity of sorts. Maintaiining a sense of our need to become better and appreciation of othersâ?? greater talents is also a way to maintain healthy humility. I think Iâ??m up for mediocrity ? in a wonder-filled, amazing sort of way.





__._,_.___

Posted by: Jean Marais <jeannieboef@xxxxxxxxx>


EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The EnergyPlus web site is found at:
http://www.energyplus.net/

The group web site is:
http://groups..yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the &quot;search&quot; button.




Visit Your Group
Yahoo! Groups
• Privacy • Unsubscribe • Terms of Use

__,_._,___