When you define an airflow network, properties like the air change
rate are *emergent*, that is, they result from the interaction of the
flow drivers (wind, temperature, ventilation components) and the flow
limiters (resistance to flow in the different paths).

That means there isn't an "upper limit dial" you can use to
artificially enforce some maximum ACR the model predicts.

Instead, if your model predicts an unrealistically high airflow, you
should look to the model definition.  What flow elements are defined?
How are they parameterized?  What airflow drivers are they responding
to?

-Dave

> I used the AirflowNetwork objects to simulate a naturally ventilated Greenhouse.
> First results are in and everything works fine appart from the fact that I cannot seem to limit the maximum ventilation rate. At some points I get infiltration air change rates of 136 1/h.
> I would like to limit the air change rates to a maximum of 30.
> Is that possible? Should I do it via schedule or another object? In the objects that I've used the only defineable upper limit that I could find is the Enthalpy difference. I don't really know if control through enthalpy is the right way?


------------------------------------
Posted by: David Lorenzetti <dmlorenzetti@xxxxxxx>
------------------------------------

EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The EnergyPlus web site is found at:
http://www.energyplus.net/

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the &quot;search&quot; button.
------------------------------------

Yahoo Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo Groups is subject to:
    https://info.yahoo.com/legal/us/yahoo/utos/terms/