Hi,

Recently, we were involved in a project where DOAS exhaust is being used to heat the basement during the winter season. In order to model it, we created a separate AHU (DOAS) for the basement and Air volume/temp from the Exhaust DOAS was assigned to it by creating a Schedule:File. There were some more controls based on the zone  air temperature which we addressed through EMS. It worked quite well at the end. 

Sharing screenshot of epw based outdoor Air vs. Custom Outdoor Air Node created for Basement DOAS

image.png

Not sure if this was helpful.

thank you, 

On Mon, Aug 3, 2020 at 12:00 PM Jean Marais jeannieboef@xxxxxxxxx [EnergyPlus_Support] <EnergyPlus_Support@xxxxxxxxxxxxxxx> wrote:
 

Hi guys,
Do you know of a way to couple an exhaust only zone (makeup air via zone mixing object) to a central AHU?

I have the overflow from office zones spilling over into a central atrium that is the main exhaust point to bring the air back to the central AHU. I can use zone exhaust fan objects and zone mixing objects to reduce the extract air in the office zones and shift the office air into the atrium at the extract temperature, but I don't see how I can create an airloop for the atrium with zero supply and really large exhaust. It would be required to get the even warmer air temperature of the air accounted for in the heat recovery of the central air handling unit..

Any suggestions?

Jean



--

Technical Specialist Energy Modeling 

ECBC Expert Professional









__._,_.___

Posted by: Javed Iqbal <eee.javed@xxxxxxxxx>


EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The EnergyPlus web site is found at:
http://www.energyplus.net/

The group web site is:
http://groups..yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the &quot;search&quot; button.




Visit Your Group
Yahoo! Groups
• Privacy • Unsubscribe • Terms of Use

__,_._,___