[Equest-users] eQUEST building skin effects in cooling but not heating

Brian Davis BDavis at dwyer.com
Thu Dec 4 08:44:26 PST 2008


I am using the refrigeration version of equest 3.61 and have several zones within the building which have exterior walls and roof.  The equest output notes loads in cooling for them but not in heating while other zones properly indicate loads for both cooling and heating, has anyone else run across this and can suggest something for me to check.  The output is listed below.




REPORT- LS-B Space Peak Load Components     EL1 NNE Perim Spc (G.NNE16)                     WEATHER FILE- Baltimore    MD TMY2

---------------------------------------------------------------------------------------------------------------------------------



SPACE  EL1 NNE Perim Spc (G.NNE16)

SPACE TEMPERATURE USED FOR THE LOADS CALCULATION IS   70 F /  21 C





                    MULTIPLIER        1.0          FLOOR MULTIPLIER        1.0



                    FLOOR  AREA     28544  SQFT      2652   M2

                    VOLUME         513785  CUFT     14550   M3





                                          COOLING  LOAD                               HEATING  LOAD

                                     ==========================                ==========================

    TIME                                    AUG  3  7PM



    DRY-BULB TEMP                      93 F             34 C

    WET-BULB TEMP                      76 F             24 C

    TOT HORIZONTAL SOLAR RAD           80 BTU/H.SQFT   252 W/M2

    WINDSPEED AT SPACE                5.3 KTS          2.7 M/S

    CLOUD AMOUNT 0(CLEAR)-10            0







                                  SENSIBLE            LATENT                              SENSIBLE

                            (KBTU/H)    ( KW )  (KBTU/H)  ( KW )                     (KBTU/H)  ( KW )

                            --------    ------  --------  ------                     --------  --------



     WALL CONDUCTION           4.394     1.287     0.000   0.000                        0.000     0.000

     ROOF CONDUCTION          28.204     8.264     0.000   0.000                        0.000     0.000

     WINDOW GLASS+FRM COND     0.000     0.000     0.000   0.000                        0.000     0.000

     WINDOW GLASS SOLAR        0.000     0.000     0.000   0.000                        0.000     0.000

     DOOR CONDUCTION           0.000     0.000     0.000   0.000                        0.000     0.000

     INTERNAL SURFACE COND     0.000     0.000     0.000   0.000                        0.000     0.000

     UNDERGROUND SURF COND    -0.666    -0.195     0.000   0.000                        0.000     0.000

     OCCUPANTS TO SPACE       18.451     5.406    15.444   4.525                        0.000     0.000

     LIGHT     TO SPACE      144.060    42.209     0.000   0.000                        0.000     0.000

     EQUIPMENT TO SPACE        0.000     0.000     0.000   0.000                        0.000     0.000

     PROCESS   TO SPACE        0.000     0.000     0.000   0.000                        0.000     0.000

     INFILTRATION              1.692     0.496     2.090   0.612                        0.000     0.000

                            --------   -------   -------  ------                     --------  --------

     TOTAL                   196.134    57.467    17.534   5.137                        0.000     0.000

     TOTAL / AREA              0.007     0.022     0.001   0.002                        0.000     0.000



     TOTAL LOAD              213.669 KBTU/H       62.605  KW                  0.000 KBTU/H        0.000  KW

     TOTAL LOAD / AREA         7.49  BTU/H.SQFT   23.609  W/M2                0.000 BTU/H.SQFT    0.000  W/M2