[Equest-users] eQUEST building skin effects in cooling but notheating
Gary.Schrader at tac.com
Gary.Schrader at tac.com
Thu Dec 4 08:51:52 PST 2008
Brian,
You have a significant amount of light and occupant load in your
building. Are you using a heating design day? Does that design day call
for a heating design day schedule? Does that heating design day schedule
shut down the lights/occupants during the course of the day such that no
light/occupant load is contributed to the space during the heating
season?
My prediction is that your lights/occupants/etc. are still scheduled
during the winter months and thus your building doesn't NEED heat. Check
your schedules to ensure that the above items are "off" during the
winter months such that the room isn't heating itself.
Another way to prove this would be to run an hourly report and check to
see if your cooling coil(s) is/are in use during all days of the year.
Just an idea of where to start.
Thanks,
Gary Schrader
Engineer I
TAC
16011 College Blvd, Suite 212
Lenexa, KS 66219
Direct: +1
Fax: +1 913-469-0206
Mobile: +1 913-217-8068
Email: Gary.Schrader at tac.com
Web: www.tac.com <http://www.tac.com/>
Notice: This email message, together with any attachments, contains
information of TAC, which may be confidential, proprietary, copyrighted
and/or legally privileged. This email is intended solely for the use of
the individual or entity named on the message. If you are not the
intended recipient, and have received this message in error, please
immediately return by email and then delete it.
________________________________
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Brian
Davis
Sent: Thursday, December 04, 2008 10:44 AM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] eQUEST building skin effects in cooling but
notheating
I am using the refrigeration version of equest 3.61 and have several
zones within the building which have exterior walls and roof. The
equest output notes loads in cooling for them but not in heating while
other zones properly indicate loads for both cooling and heating, has
anyone else run across this and can suggest something for me to check.
The output is listed below.
REPORT- LS-B Space Peak Load Components EL1 NNE Perim Spc (G.NNE16)
WEATHER FILE- Baltimore MD TMY2
------------------------------------------------------------------------
---------------------------------------------------------
SPACE EL1 NNE Perim Spc (G.NNE16)
SPACE TEMPERATURE USED FOR THE LOADS CALCULATION IS 70 F / 21 C
MULTIPLIER 1.0 FLOOR MULTIPLIER
1.0
FLOOR AREA 28544 SQFT 2652 M2
VOLUME 513785 CUFT 14550 M3
COOLING LOAD
HEATING LOAD
==========================
==========================
TIME AUG 3 7PM
DRY-BULB TEMP 93 F 34 C
WET-BULB TEMP 76 F 24 C
TOT HORIZONTAL SOLAR RAD 80 BTU/H.SQFT 252 W/M2
WINDSPEED AT SPACE 5.3 KTS 2.7 M/S
CLOUD AMOUNT 0(CLEAR)-10 0
SENSIBLE LATENT
SENSIBLE
(KBTU/H) ( KW ) (KBTU/H) ( KW )
(KBTU/H) ( KW )
-------- ------ -------- ------
-------- --------
WALL CONDUCTION 4.394 1.287 0.000 0.000
0.000 0.000
ROOF CONDUCTION 28.204 8.264 0.000 0.000
0.000 0.000
WINDOW GLASS+FRM COND 0.000 0.000 0.000 0.000
0.000 0.000
WINDOW GLASS SOLAR 0.000 0.000 0.000 0.000
0.000 0.000
DOOR CONDUCTION 0.000 0.000 0.000 0.000
0.000 0.000
INTERNAL SURFACE COND 0.000 0.000 0.000 0.000
0.000 0.000
UNDERGROUND SURF COND -0.666 -0.195 0.000 0.000
0.000 0.000
OCCUPANTS TO SPACE 18.451 5.406 15.444 4.525
0.000 0.000
LIGHT TO SPACE 144.060 42.209 0.000 0.000
0.000 0.000
EQUIPMENT TO SPACE 0.000 0.000 0.000 0.000
0.000 0.000
PROCESS TO SPACE 0.000 0.000 0.000 0.000
0.000 0.000
INFILTRATION 1.692 0.496 2.090 0.612
0.000 0.000
-------- ------- ------- ------
-------- --------
TOTAL 196.134 57.467 17.534 5.137
0.000 0.000
TOTAL / AREA 0.007 0.022 0.001 0.002
0.000 0.000
TOTAL LOAD 213.669 KBTU/H 62.605 KW
0.000 KBTU/H 0.000 KW
TOTAL LOAD / AREA 7.49 BTU/H.SQFT 23.609 W/M2
0.000 BTU/H.SQFT 0.000 W/M2
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20081204/a38f697a/attachment-0001.htm>
More information about the Equest-users
mailing list